tell me about vfd
Answers were Sorted based on User's Feedback
I know only abbr. of VFD Variable frequency Drive
| Is This Answer Correct ? | 6 Yes | 0 No |
The main purpose of VFD is to control the speed of the motor
in general if u take an induction motor its speed can be
changed either by voltage or by frequency if we made voltage
alone variable also speed will change but only up to certain
point on the other hand if speed control is achieved by
frequency speed control is only possible up to certain
limits beyond that the flux will be saturated
The best method is to control the speed by means both
voltage and frequency but keeping their ratio constant
this can be achieved by means of scr (semi controlled
rectifier) vfd is a closed loop system it takes the feedbsck
of speed from the motor (Tacho genrator or Current Fb)and
adjusts the firing of scr accordingly
Now a days in modern technology Converter or inverter
circuit is 6 pulse or 12 pulse depending on the application
| Is This Answer Correct ? | 5 Yes | 0 No |
Answer / sankar maiti
VFD Variable Frequency drive. Frequency change also will be
change speed . analog input supply 4- 20 ma through plc to
be change speed and out commend 4-20 ma swing in your scada
on your pc.start stop comment through digital comment.start
to out side the field.
| Is This Answer Correct ? | 4 Yes | 1 No |
Answer / gulshan
VFD Variable Frequency drive. Frequency change also will be
change speed . analog input supply 4- 20 ma through plc to
be change speed and out commend 4-20 ma swing in your scada
on your pc.start stop comment through digital comment.start
to out side the field.
But we can also control the motor with VFD with a
POtentiometer. We can use the poentiometer instead of PLC.
It also can vary the Frequency
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / anup patil
VFD stands for Variable Frequency drive or Variable speed
drive.It is mainly used to change the speed of the motor
from 0Hz to rated Hz of the motor.By doing this you can
operate the motor at variable speed.The advantage of using
vfd in the system to save power by almost 305.It depends on
which type of applications you are using it.
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / ashok
VFD stands for Variable Frequency drive we can not incress
the motor rated speed and Frequency IF (1450 RPM & 50HZ)
Any application start from zero RPM to requied as demands.
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / nitin pathak
Basically a VFD consists of 3 main components
1)six-pulse rectifier that converts three phase AC voltage
to DC voltage
2)capacitior bank for energy storage which stabilizes the
intermediate circuit DC voltage.
3)six-pulse IGBT inverter that converts the DC voltage to
AC voltage and vice versa.
The motor operation is controlled by changing the firing
angle(switching) of the IGBTs
Nitin Pathak
Lafarge Cement
| Is This Answer Correct ? | 2 Yes | 1 No |
Answer / baskaran.p
Variable frequency drive:
We can run the Motor and control the speed through plc,
SCADA & Potentiometer.
V
we can run the motor through digital input 24 voltage and
we can run 4-20mA
| Is This Answer Correct ? | 0 Yes | 0 No |
what is the function of breather in a transformer
29 Answers Areva, Bhel, RKM Powergen, Vijai Electricals,
what is the essential resistance of r y b phase short citcuit ? Eg in star connection we doing this kind of short circuit oly
We have 2 Nos. Transformer with the capacity of 2000KVA and 1250 KVA and currently using only one 2000KVA T/R during operational hours while non- operational hous 1250 KVA T/R also used to reduce T & D losses. Similarly, 2 capacitor bank of 500KVAR and 300 KVAR also installed to balance reactive power. Now problem is around 1000 KW load PF is not maintaning 0.99 as 350 KVAR capacitor is in healty condtion. Now the PF is maintain 0.95 to 0.96.
why transformer rating in kva
Why the colour of insulator is always is chocolate in colour?
In Extended Delta transformer, by which method we can measure the extended angle of transformer?
I HAVE A INCOMING 100A MCCB TPN 25KA, CABLE LENGHT OF 80M 70MM CABLE SIZE FROM MAIN SUBBOARD TO NEW DB.BASE ON THE FAULT LEVEL SETTING OF 45KA.I WOULD LIKE TO FIND OUT 25KA ENOUGH KA. APPRECIATE IF SOMEBODY CAN ASSIST ME WITH FORMULA FOR THIS. FRM: JEFF
why the electrolyte level in lead acid battery is maintained 2.5 cms above electrodes?
IF I USED VVVF DRIVE IN FAN APPLICATION MOTOR IN 6.6 KV ( 700 KW) MOTOR & DURING NORMAL RUN OPERATION TIME IF RPM SUDDENLY REDUCE IN MOTOR BY DRIVE(E. MOTOR RPM REDUCE SUDENLY 687 TO 550 RPM) WAHT WILL BE HAPPEND IN DRIVE
Make a list of materials and layout diagram for a 35hp motor, to be wired at 35meter away from the MDB in a chemical factory.
why transformer is giving some humming noise .....?
Are you connected Transformer neutral eathing with it's body earthing or earthing met of switch yard.? Yes or No ? why ?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)