tell me about vfd
Answers were Sorted based on User's Feedback
I know only abbr. of VFD Variable frequency Drive
Is This Answer Correct ? | 6 Yes | 0 No |
The main purpose of VFD is to control the speed of the motor
in general if u take an induction motor its speed can be
changed either by voltage or by frequency if we made voltage
alone variable also speed will change but only up to certain
point on the other hand if speed control is achieved by
frequency speed control is only possible up to certain
limits beyond that the flux will be saturated
The best method is to control the speed by means both
voltage and frequency but keeping their ratio constant
this can be achieved by means of scr (semi controlled
rectifier) vfd is a closed loop system it takes the feedbsck
of speed from the motor (Tacho genrator or Current Fb)and
adjusts the firing of scr accordingly
Now a days in modern technology Converter or inverter
circuit is 6 pulse or 12 pulse depending on the application
Is This Answer Correct ? | 5 Yes | 0 No |
Answer / sankar maiti
VFD Variable Frequency drive. Frequency change also will be
change speed . analog input supply 4- 20 ma through plc to
be change speed and out commend 4-20 ma swing in your scada
on your pc.start stop comment through digital comment.start
to out side the field.
Is This Answer Correct ? | 4 Yes | 1 No |
Answer / gulshan
VFD Variable Frequency drive. Frequency change also will be
change speed . analog input supply 4- 20 ma through plc to
be change speed and out commend 4-20 ma swing in your scada
on your pc.start stop comment through digital comment.start
to out side the field.
But we can also control the motor with VFD with a
POtentiometer. We can use the poentiometer instead of PLC.
It also can vary the Frequency
Is This Answer Correct ? | 2 Yes | 0 No |
Answer / anup patil
VFD stands for Variable Frequency drive or Variable speed
drive.It is mainly used to change the speed of the motor
from 0Hz to rated Hz of the motor.By doing this you can
operate the motor at variable speed.The advantage of using
vfd in the system to save power by almost 305.It depends on
which type of applications you are using it.
Is This Answer Correct ? | 2 Yes | 0 No |
Answer / ashok
VFD stands for Variable Frequency drive we can not incress
the motor rated speed and Frequency IF (1450 RPM & 50HZ)
Any application start from zero RPM to requied as demands.
Is This Answer Correct ? | 2 Yes | 0 No |
Answer / nitin pathak
Basically a VFD consists of 3 main components
1)six-pulse rectifier that converts three phase AC voltage
to DC voltage
2)capacitior bank for energy storage which stabilizes the
intermediate circuit DC voltage.
3)six-pulse IGBT inverter that converts the DC voltage to
AC voltage and vice versa.
The motor operation is controlled by changing the firing
angle(switching) of the IGBTs
Nitin Pathak
Lafarge Cement
Is This Answer Correct ? | 2 Yes | 1 No |
Answer / baskaran.p
Variable frequency drive:
We can run the Motor and control the speed through plc,
SCADA & Potentiometer.
V
we can run the motor through digital input 24 voltage and
we can run 4-20mA
Is This Answer Correct ? | 0 Yes | 0 No |
How can we calculate the capacitance of generator?
What are the different types of testing in ht cables?
Explain What will happen when direction of field current is changed (i.e, field excitation is reversed) in the following machines? 1) Alternator 2) Synchronous Motor 3) D.C Generator ( Shunt or Seies ) 4) D.C Motor ( Shunt or Seies )
How to calculate the cross section area for a 350 m cable, motor power is 26 kw???
Is it required to lay 2 runs of GI wires along with armoured cables from one power DB Machines of higher rating?
what is the different between RCCB & ELCB
What is the acceptance value of leakage current in HI POT test
a wire in which bulb is connected there is two terminal when one terminal is connected to phase than why the value of current shock in nutral terminal is max. or large??
why use only sf6 circuit breker in 400 kv sub station
how to select the no. of brushes in a lap winding?
what is the function of potential transformer in s/s
Whether the vacuum contactor requires Short circuit protection?If No,why?