Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


why should we place 9KV lightning arrestors in 11KV
substation ?

Answers were Sorted based on User's Feedback



why should we place 9KV lightning arrestors in 11KV substation ?..

Answer / mohan rao

Lightning arrestors are always placed between line and
Gronund. Line to Ground Voltage of a 11 kV System is 6.35
kV. The lighning arrestoer rating should be above this
level but below 11 kV so that 9 kV arrestor is suitable.

Is This Answer Correct ?    114 Yes 10 No

why should we place 9KV lightning arrestors in 11KV substation ?..

Answer / d. bhowmick

All power system devices are designed with certain
tolarence limits.This is because it is always desirable
that the equipments/devices can withstand transient
voltage/current rise without any damage up to a certain
preset limit.
For an 11 KV line, the effective phase to ground voltage is
6.35 KV. That is, an LA associated with this line(between
the phases & ground)is supposed to operate when the system
voltage exceeds 6.35 KV. However, in many cases the system
voltage may momentarily rise above this value owing to
switching action or induction-that can easily be tolarated
by the associated equipments(having their individual
tolarances). Under this circumstance, it is desirable that
the LA donot unnecessarily operate especially when the rise
in voltage is within the tolance limit of the associated
equipments. To enable this, LAs with slightly higher value
of voltage rating are provided for a system operating at a
certain system voltage. Clearly, for a 6.35 KV(L-G)system
associated with a 9 KV LA, no damage is expected to be
caused if the system voltage rises by a maximum of 2.65 KV.
Beyond this, the LAs will come into action.

Is This Answer Correct ?    46 Yes 1 No

why should we place 9KV lightning arrestors in 11KV substation ?..

Answer / amit

The system voltage is always specified in RMS value or we can say that we can measure only RMS value but actually the system is subjected to peak voltage. in case of 11 kv system if the LA is provided between line to neutral, which is normally the case is, the phase value will be 11kv/sqrt(3)= 6.35kv (the phase value. but the peak value for this phase voltage will be sqrt(2)*6.35kv = 8.98kv. hence the rating of LA will be 9kv

Is This Answer Correct ?    46 Yes 1 No

why should we place 9KV lightning arrestors in 11KV substation ?..

Answer / a.umapathy

The reason is when ligtning impulse is more than 9kV the
lightning arrestor by pass the lightning impuluse so that
the 11kV system will be affected. If lightning arrestor
rating is more than the system working voltage (say 15kV)
then 11kV system will experience higher voltage which will
cause the damage in apparatus (as this designed for 11kV).
So insulation coordination of protective device must be
less than the device to be protected.

Is This Answer Correct ?    52 Yes 30 No

why should we place 9KV lightning arrestors in 11KV substation ?..

Answer / neelesh gupta

The most simple funda for calculating LA Rating-

LA Rating = Rated Line Voltage* (Square Root 2) / (Square
Root 3)

To be more precise-

LA Rating = Rated line voltage*1.414/1.732

Suggestions welcome @ neel.kewl@gmail.com

Is This Answer Correct ?    29 Yes 11 No

why should we place 9KV lightning arrestors in 11KV substation ?..

Answer / ganika

Lightning arrestors are always connected between line to
earth. Line to earth Voltage of a 11 kV System is 6.35
kV. The lightning arrestors voltage grade also same, But we are selecting the Standard, suitable, and safe apparatus availability in the market.

Is This Answer Correct ?    2 Yes 2 No

why should we place 9KV lightning arrestors in 11KV substation ?..

Answer / gagan

SAME AS ABOVE

Is This Answer Correct ?    1 Yes 12 No

why should we place 9KV lightning arrestors in 11KV substation ?..

Answer / mohan

THE L.A USED FOR 11KV SYSTEM IS 9KV BCOZ IT OPERATE AT 9KV
OR ABOVE IF WE USE L.A OF HIGHER RATING (15KV) THEN IF
VOLTAGE SURGE OF 14.5 IS PRODUCED THEN OUR LA WILL NOT
OPERATE AND PROTECTION FAIL AND HIGH VOLTAGE SURGR DAMAGE
THE SYSTEM

Is This Answer Correct ?    2 Yes 22 No

why should we place 9KV lightning arrestors in 11KV substation ?..

Answer / virender

The LA are designed to by pass the high voltage surges so
that the system voltages do not get affected and the
equipment in line are safe. We place 9kv in 11kv substation
becouse it can attract the lightning surges in the 11KV
system with low resistance and can ground quickly.

If anyone want to add more he is welcome.

Is This Answer Correct ?    11 Yes 33 No

Post New Answer

More Electrical Engineering Interview Questions

Draw a circuit diagram in which if button is open we can use socket and bulb as a series test circit and if button is close than simple we can use socket as any load purpose.

0 Answers  


Which is is best option for 33 kv line incomer.I am Desinging the panel for new projects and i would like to get Your opinion on this Vcb or sf6. Please help me with your replies. Thanks D p singh

6 Answers  


why we are using the 2 slope in differential relay?but in busbar differential we are using only one slope. what is the reason.

1 Answers  


TNC switch is also available in 1NO+1NC. What does it mean ?

1 Answers  


what is the difference between scaler and vector control in drive and where it is to be used ?

1 Answers   Essar, TCS,


What is industrial automation ??????

5 Answers  


10 tube light connect in mcb breaker.one tube light is fault.so breaker is tribe.how fault is rectified.(using 3wire phase,earth,neutral)

0 Answers   CTS, Jindal,


When in a large power system if the demand of power is larger than the generated power the frequency of the power system drops.(assume the rated frequency is 50Hz and now it is 49Hz) So does this mean the demand is totally supplied with a lower value of generated power in a lower frequency?

1 Answers  


can u guys pls suggest a good material for learning abt switch yard and its components

2 Answers  


what sq.mm copper pvc wire need for ac load current 25amps for 230v ?

4 Answers   Khadamat, Siemens,


What is the make of breakers, transformers, generators? What are their capacities and ratings?

1 Answers  


what is earthing.how we make it,describe briefly.

0 Answers   HAL,


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4453)
  • Electrical Engineering Interview Questions Electrical Engineering (16638)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)