why should we place 9KV lightning arrestors in 11KV
substation ?

Answers were Sorted based on User's Feedback



why should we place 9KV lightning arrestors in 11KV substation ?..

Answer / mohan rao

Lightning arrestors are always placed between line and
Gronund. Line to Ground Voltage of a 11 kV System is 6.35
kV. The lighning arrestoer rating should be above this
level but below 11 kV so that 9 kV arrestor is suitable.

Is This Answer Correct ?    114 Yes 9 No

why should we place 9KV lightning arrestors in 11KV substation ?..

Answer / d. bhowmick

All power system devices are designed with certain
tolarence limits.This is because it is always desirable
that the equipments/devices can withstand transient
voltage/current rise without any damage up to a certain
preset limit.
For an 11 KV line, the effective phase to ground voltage is
6.35 KV. That is, an LA associated with this line(between
the phases & ground)is supposed to operate when the system
voltage exceeds 6.35 KV. However, in many cases the system
voltage may momentarily rise above this value owing to
switching action or induction-that can easily be tolarated
by the associated equipments(having their individual
tolarances). Under this circumstance, it is desirable that
the LA donot unnecessarily operate especially when the rise
in voltage is within the tolance limit of the associated
equipments. To enable this, LAs with slightly higher value
of voltage rating are provided for a system operating at a
certain system voltage. Clearly, for a 6.35 KV(L-G)system
associated with a 9 KV LA, no damage is expected to be
caused if the system voltage rises by a maximum of 2.65 KV.
Beyond this, the LAs will come into action.

Is This Answer Correct ?    46 Yes 1 No

why should we place 9KV lightning arrestors in 11KV substation ?..

Answer / amit

The system voltage is always specified in RMS value or we can say that we can measure only RMS value but actually the system is subjected to peak voltage. in case of 11 kv system if the LA is provided between line to neutral, which is normally the case is, the phase value will be 11kv/sqrt(3)= 6.35kv (the phase value. but the peak value for this phase voltage will be sqrt(2)*6.35kv = 8.98kv. hence the rating of LA will be 9kv

Is This Answer Correct ?    45 Yes 1 No

why should we place 9KV lightning arrestors in 11KV substation ?..

Answer / a.umapathy

The reason is when ligtning impulse is more than 9kV the
lightning arrestor by pass the lightning impuluse so that
the 11kV system will be affected. If lightning arrestor
rating is more than the system working voltage (say 15kV)
then 11kV system will experience higher voltage which will
cause the damage in apparatus (as this designed for 11kV).
So insulation coordination of protective device must be
less than the device to be protected.

Is This Answer Correct ?    52 Yes 30 No

why should we place 9KV lightning arrestors in 11KV substation ?..

Answer / neelesh gupta

The most simple funda for calculating LA Rating-

LA Rating = Rated Line Voltage* (Square Root 2) / (Square
Root 3)

To be more precise-

LA Rating = Rated line voltage*1.414/1.732

Suggestions welcome @ neel.kewl@gmail.com

Is This Answer Correct ?    28 Yes 11 No

why should we place 9KV lightning arrestors in 11KV substation ?..

Answer / ganika

Lightning arrestors are always connected between line to
earth. Line to earth Voltage of a 11 kV System is 6.35
kV. The lightning arrestors voltage grade also same, But we are selecting the Standard, suitable, and safe apparatus availability in the market.

Is This Answer Correct ?    2 Yes 2 No

why should we place 9KV lightning arrestors in 11KV substation ?..

Answer / gagan

SAME AS ABOVE

Is This Answer Correct ?    1 Yes 12 No

why should we place 9KV lightning arrestors in 11KV substation ?..

Answer / mohan

THE L.A USED FOR 11KV SYSTEM IS 9KV BCOZ IT OPERATE AT 9KV
OR ABOVE IF WE USE L.A OF HIGHER RATING (15KV) THEN IF
VOLTAGE SURGE OF 14.5 IS PRODUCED THEN OUR LA WILL NOT
OPERATE AND PROTECTION FAIL AND HIGH VOLTAGE SURGR DAMAGE
THE SYSTEM

Is This Answer Correct ?    2 Yes 22 No

why should we place 9KV lightning arrestors in 11KV substation ?..

Answer / virender

The LA are designed to by pass the high voltage surges so
that the system voltages do not get affected and the
equipment in line are safe. We place 9kv in 11kv substation
becouse it can attract the lightning surges in the 11KV
system with low resistance and can ground quickly.

If anyone want to add more he is welcome.

Is This Answer Correct ?    11 Yes 33 No

Post New Answer

More Electrical Engineering Interview Questions

How to calculate of maximum demand if given 628kw, 785kva, 0.8 p.f.

0 Answers  


what is the diffrence between R Y B phase and why it is called RYB

5 Answers  


what is use of thermistor ?

2 Answers  


What is resistance reading of earth copper rod with grid and without grid?

0 Answers  


In our factory there is one no. of Series trip HT 6KV OCB. 1. Is it possible to measure CT out put current by 440V Clamp meter? The measurement is required for knowing the exact value of current in CT secondary to set up protection for transformers. 2. plase forward the single line diagram of AMF panel?

1 Answers   HAL,






what is the mechanism of operation of brushless dc motor why is it more wexpensive then ordinary permanent magnet motors

0 Answers   Lanco,


why a diode bridge is provided in vcb control circuit ?

2 Answers  


why active power is called as real power or working component.What is the exact function of active, reactive & apperent power.

3 Answers  


Which type of a.c motor is used in the fan (ceiling fan, exhaust fan, pedestal fan, bracket fan etc) which are find in the houses ?

0 Answers  


temp of cast resin 1500kva tx formerwent up to 138.c but came down very fast to about 100.c within 20 mins when load was reduced from 70% to 60%

0 Answers  


11KV AND 22KV NETWORK KW CAPACITY IN RING AND RADIAL?

0 Answers   BK Gulf,


Why do we use series motor to start our car?

2 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4451)
  • Electrical Engineering Interview Questions Electrical Engineering (16632)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)