why should we place 9KV lightning arrestors in 11KV
substation ?
Answers were Sorted based on User's Feedback
Answer / mohan rao
Lightning arrestors are always placed between line and
Gronund. Line to Ground Voltage of a 11 kV System is 6.35
kV. The lighning arrestoer rating should be above this
level but below 11 kV so that 9 kV arrestor is suitable.
| Is This Answer Correct ? | 114 Yes | 10 No |
Answer / d. bhowmick
All power system devices are designed with certain
tolarence limits.This is because it is always desirable
that the equipments/devices can withstand transient
voltage/current rise without any damage up to a certain
preset limit.
For an 11 KV line, the effective phase to ground voltage is
6.35 KV. That is, an LA associated with this line(between
the phases & ground)is supposed to operate when the system
voltage exceeds 6.35 KV. However, in many cases the system
voltage may momentarily rise above this value owing to
switching action or induction-that can easily be tolarated
by the associated equipments(having their individual
tolarances). Under this circumstance, it is desirable that
the LA donot unnecessarily operate especially when the rise
in voltage is within the tolance limit of the associated
equipments. To enable this, LAs with slightly higher value
of voltage rating are provided for a system operating at a
certain system voltage. Clearly, for a 6.35 KV(L-G)system
associated with a 9 KV LA, no damage is expected to be
caused if the system voltage rises by a maximum of 2.65 KV.
Beyond this, the LAs will come into action.
| Is This Answer Correct ? | 46 Yes | 1 No |
Answer / amit
The system voltage is always specified in RMS value or we can say that we can measure only RMS value but actually the system is subjected to peak voltage. in case of 11 kv system if the LA is provided between line to neutral, which is normally the case is, the phase value will be 11kv/sqrt(3)= 6.35kv (the phase value. but the peak value for this phase voltage will be sqrt(2)*6.35kv = 8.98kv. hence the rating of LA will be 9kv
| Is This Answer Correct ? | 46 Yes | 1 No |
Answer / a.umapathy
The reason is when ligtning impulse is more than 9kV the
lightning arrestor by pass the lightning impuluse so that
the 11kV system will be affected. If lightning arrestor
rating is more than the system working voltage (say 15kV)
then 11kV system will experience higher voltage which will
cause the damage in apparatus (as this designed for 11kV).
So insulation coordination of protective device must be
less than the device to be protected.
| Is This Answer Correct ? | 52 Yes | 30 No |
Answer / neelesh gupta
The most simple funda for calculating LA Rating-
LA Rating = Rated Line Voltage* (Square Root 2) / (Square
Root 3)
To be more precise-
LA Rating = Rated line voltage*1.414/1.732
Suggestions welcome @ neel.kewl@gmail.com
| Is This Answer Correct ? | 29 Yes | 11 No |
Answer / ganika
Lightning arrestors are always connected between line to
earth. Line to earth Voltage of a 11 kV System is 6.35
kV. The lightning arrestors voltage grade also same, But we are selecting the Standard, suitable, and safe apparatus availability in the market.
| Is This Answer Correct ? | 2 Yes | 2 No |
Answer / mohan
THE L.A USED FOR 11KV SYSTEM IS 9KV BCOZ IT OPERATE AT 9KV
OR ABOVE IF WE USE L.A OF HIGHER RATING (15KV) THEN IF
VOLTAGE SURGE OF 14.5 IS PRODUCED THEN OUR LA WILL NOT
OPERATE AND PROTECTION FAIL AND HIGH VOLTAGE SURGR DAMAGE
THE SYSTEM
| Is This Answer Correct ? | 2 Yes | 22 No |
The LA are designed to by pass the high voltage surges so
that the system voltages do not get affected and the
equipment in line are safe. We place 9kv in 11kv substation
becouse it can attract the lightning surges in the 11KV
system with low resistance and can ground quickly.
If anyone want to add more he is welcome.
| Is This Answer Correct ? | 11 Yes | 33 No |
How will I know that how many batteries I should connect to my UPS unit?
what is the difference between earthed system and unearthed system.. where do we use unearthed system because in electrical catalogues always cable for earthed and unearthed system is given..pls elaborate
what is the carona effects meaning in HT line transmmission system
why we measure ouput of transformers in kva.
When alarm is activated in buccholz relay in transformer
what type of earthing do for dry fissure rock?
what will be the min and max voltage flow from neutral to earth?
Dear Sir / Madam, Actually we requied 64 A MCB, But i have 32 A MCB = 2 No's this two i have to make series connection and we usw any place? isit possible or not......
4 Answers Hindustan Unilever Limited,
different between grounding & earthing?
what is corona
HAI,I HAVE 6,60KW MOTOR FEEDERS IN MY MCC PANEL.HOW CAN I DO MY SETTINGS FOR OVERLOAD,SHORTCIRCUIT,GROUNGFAULT,INSTANTANEOUS TRIP FUNCTION IN MY 4000A CIRCUIT BREAKER?
what is IP55,IP65
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)