why does a transmitter o/o signal starts from 3-15psi or 4-
20mA?
Answers were Sorted based on User's Feedback
Answer / priyabeet das
1st of all this is a live zero concept. now what is live zero? suppose the range is 0-20ma.so the Tx will indicate0ma as lower value.but when there is no i/p or there is some fault in process then also Tx will show 0ma as reading. so , seeing 0ma we cant decide whether it is for any i/p or not. that is why the lower LRV is chosen as 4ma.
| Is This Answer Correct ? | 14 Yes | 2 No |
Answer / suresh
This is Live zero concept. In case of airsupply failure or
Current loop failure the Control equipment (DCS/PLC) senses
below 3.5mA, considered as Loop Open circuit.
| Is This Answer Correct ? | 13 Yes | 4 No |
Answer / sudipta,iter
bcz 4 ma is the amount of current that occurs when there is
no input to the transmistter and coresponding pressure is
3psi.this is called as live zero concept.so by using thus
we can detect error easily .thats why we usese this value.
| Is This Answer Correct ? | 10 Yes | 4 No |
Answer / oza paritosh m.
It is also useful for instrumentation guy to differentiate
between process zero and instrument zero.
| Is This Answer Correct ? | 3 Yes | 1 No |
Answer / abu maryam
For 4 mA & 3 Psi it is virtual zero to differ with actual zero (0 mA & 0 psi) to define if actual signal (mA & air )is found or not.
For 4: 20 mA
In my opinion the reason for use these values is most electronic cards work from 1: 5 volt and resistance (hart ) is 250 ohm
then V=I * R
R= 250 ohm and V= 1 volt so I= 1/250=,004 A= 4 mA
R= 250 ohm and V= 5 volt so I= 4/250=,02 A= 20 mA
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / dr
Why not more than 20ma??
More than 20ma continuously for 20Sec will make your heart
to malfunction.
| Is This Answer Correct ? | 2 Yes | 4 No |
Answer / prashant jadhav
If we look at Hazardous and power consumption point, 4-20 mA is the perfect range qualifying both points...Not able to produce large sparks and consumes least power...So it is made as a Standard signal..
| Is This Answer Correct ? | 0 Yes | 2 No |
Answer / rajesh j
4-20mA is because the least power consumption range with
linearity and to detect even when signal line opens
3-15psi is because of the minimum linear range for which
the control valve will respond to pneumatic signal
| Is This Answer Correct ? | 1 Yes | 4 No |
Answer / rafiq
these are standared things. its nothing but a i to p
converter. for 4 ma it will convert 3 psi and for 20 ma it
has 15 psi.
| Is This Answer Correct ? | 2 Yes | 8 No |
Yokogawa dcs normally where will change 4-20 MA to DC voltage( node or I/o cards?)
plz... clarify my answer, how to calibrate vaccum (DP)leveltransmitter,it is hart. (digital).DETAILS:(coloumn)closedtank height 2650mm,and tx range is 0-1500mmH20.
What is the purpose of the analyzer in petrochemical plant?
0 Answers ENI, Lakshmi Machine Works,
KAlman filter code for two dimension?
Need Intergraph softwares like SPI(INTOOLS),sp3d,PV ELITE, SP P&ID. CONTACT : logu.2211@gmail.com (8867825756)
what is isloted barrier how it works and what are the main purpose.how it make safe area.
How many interlocks at turbine side?
what is the difference between dcs & plc
Calibration procedure for water rotameters
Is it possible to convert 4 wire transmitter to convert to 2 wire with additional relay.Please send detial with drawing,i will appreciate.
WHAT ARE THE INSTRUMENTAL DIAGRAMSOF VALVES?
0 Answers Artikal, ITC Infotech,
What is expansion of SMART Instruments? And What is it?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)