why do we use 4-20mA as o/p and why don't use 0-20mA or 5-
21mA?
Answers were Sorted based on User's Feedback
Answer / ahmed eid
Ohm's law voltage = current * resistance
of the standerd voltage in the dcs from 1 to 5 voltge
and the standerd resistance of loop 250 oums
so
V=I*R
the first in the low signal 1 volt
1(v)=I*250(r) =.004 A
.004*1000 = 4 MA
the sacand in the high signal 5 volt
5(v)=I*250(r) = 020 A
.020*250 = 20 MA
| Is This Answer Correct ? | 19 Yes | 0 No |
Answer / d tilston
Two wire transmitters require some power to work. 0-20 mA
would not provide any power at 0 mA.
Power = current x volts, (usually 24 VDC)
Power = 0.004A x 24VDC
Power = 0.096W
Not much power.
| Is This Answer Correct ? | 4 Yes | 0 No |
Answer / carl_ellis
Question:
why do we use 4-20mA as o/p and why don't use 0-20mA or 5- 21mA?
There are systems that use 0-20mA as an output from a
controller. Those are active', powered outputs, not
signals from 2 wire, loop powered field transmitters. 2
wire, loop powered instruments use about 3.5mA to power the
transmitter's electronics, so 2 wire, loop powered
instruments can never go below 3.5mA without losing the
current needed to power the instrument.
An active analog output from a controller that uses the
controller's power from the controller to drive the current
signal can be a 4-20mA signal or a 0-20mA signal.
People in the process industries use the 4-20mA output
because it is a 'live-zero' that immediately indicates a
broken wire or an open circuit if the loop current falls to
0.0mA. Those using 0-20mA probably have a 0-10Vdc or 0-5Vdc
analog input and want to use the entire span with a 500 ohm
or 250 ohm resistor.
As to why 5-21mA is not used, there are conventions used
that make systems maintainable over time. If every analog
output used oddball ranges or spans, it would be near
impossible to maintain the system over time. Given that
many control systems operate in excess of 10 years, it is
important to use standard analog signals in order to keep
the system maintainable.
The convention is 4-20mA, established by the ISA SP-50
standard in 1967. Deviations are punishable. Be warned.
Carl Ellis
Measure First
| Is This Answer Correct ? | 1 Yes | 0 No |
why we use 250 ohms across HART CALIBRATOR DURING CALIBRATION OF TRANSMITTER
why do we use 4-20mA as o/p and why don't use 0-20mA or 5- 21mA?
Why do we use 24V DC supply in instrumentation? What are its merits and demerits??
What is cavitation. what is the effect of it on control valve and how is it prevented.
What is Positive Calibration and Negative Calibration?
how radio frequency level probes works with its controller ? what is its principle ? pls give me brief explanation?
wht is loops ? how many loops are there?
If range of 3-15 psi, a multiplying relay with a 1:2 ratio would give what output pressure for 6 psi input?
what is Dry Leg calibration and where is it used
how many types of orifice plates?and explain about it?
what is cold loop? difference between hot and cold loop?
Why three wire is using with a RTD?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)