How to take Transformer oil Break down voltage test?
Answer Posted / dinesh kumar
TRANSFORMER OIL BDV is carried out as per IS-336 for nomal
and IS-12463 for High viscosity oil.
1.Take one sample from top of Transformer and one from the
bottom of transformer.
2.The BDV of oil should withstood min 50 KV
3.The gap between the test sample is 2.5mm maintained
4.Each sample(top/bottom) should be checked seperately
5.Procedure
a.Voltage should be gradually increased from 0.
b. At one point Flash will take place and that point is
termed as Bread down Voltage
| Is This Answer Correct ? | 119 Yes | 10 No |
Post New Answer View All Answers
What is diversity factor in electric installations?
WHICH SIZE A.B.CABLE IS USED FOR 11KV.
On 400 amp factory load how kvarh capacitors provide
What are the factor to be consider for CT selection in 132kV substation?
what are the differences between 'exhaust fan', 'heavy-duty exhaust fan' & 'super heavy duty exhaust fan'. what are their power ratings ?
What is proportional controller?
impliment (AB)`+C to transistor representation
what is the step by step formula for calculating bus bar phase and neutral size of a panel board.suppose the incomer of panel board is 100A..???step by step answer please
Define cuttoff frequency?
What is the automatic voltage regulator with servomotor?
Why we use duplex coil and hook switch in telephone system?
what is the use of vcb & isolator in substation?
why u r living from presentaly working.
explain PV modules in solar energy generation.
what is difference between isolation and ultra isolation transformer?, what is the method of testing ?