i have 28/32 MVA power transformer with 11/6.6 KC voltage
rating and 12%impedance.it have star connection at both
side.but it have another thied winding tertiary
winding.what is used of this winding.
pl tell me
Answers were Sorted based on User's Feedback
Answer / manish meena
tertiary winding used for,
-to obtain additional voltage
-to stabilize neutral in case of star/star transformer
-to reduce third harmonics and control zero sequence
impedance.
Is This Answer Correct ? | 6 Yes | 1 No |
Answer / jnanesh
In star connected trans. third hormonics is significant so
to reduce that effect it is used.In delta connected trans.
third hormonics circulate witin and there is no effect.
Also plz note that in some substation for feeding internal
power to substation or local area this additional winding
is used.
Is This Answer Correct ? | 3 Yes | 0 No |
Answer / ajay patel
How your tertiary Winding is connected? what is the rating?
If all three phase terminals are bruoght out then it can be
used as additional seondary winding. But If this tertiary
is connected in Open Delta & 2 termianls of open delta
brought our for Earthing. That means this is installed for
Harmonic purpose. If you have rectifier, Big VFDs or such
load which can generate Theird Harmonic in big amount then
these third harmonic can be reflected in entire Grid, if
your transformer is Star - Star. Which is may damage other
equipments / consumers also who are connected with same
supply. Hence it is necessory to control 3rd harmonics in
grid. For this you can provide Delta Primary for
Transformer. But you dont have delta in primay tehn you
have to provide Tertiary winding with open Delta. This Open
delta is closed out side of Transformer & Complete Delta is
formed. This Delta winding should be earthed to minimise
harmonic disturbance in the system. Please check, do you
have earthed tertiary? Is it in Delta?
Is This Answer Correct ? | 2 Yes | 0 No |
Answer / manish jauhari
Any unbalanced loads, results in increased cirulating
current with in tertiary Delta winding, thereby keepinng
pri & sec voltages with in limits.
Is This Answer Correct ? | 2 Yes | 2 No |
Hi Paliwalsureshi,
Makers of such transformers usually provide a tertiary
winding connected in delta. This winding is sometimes called
compensating winding. As others have rightly said this
winding help to eliminate the harmoics which may interfer
with communication in power system. Before the advent of
microprocessor-based differential relays the old
differential scheme with star-star on one must have a delta
winging in between.In a nutshell any star-star connection
must have a delta tertiary.
Is This Answer Correct ? | 0 Yes | 1 No |
Why the generator rating in kva
32 Answers CompuCom, DLF, Genpact, HNG, SIPM,
which motor used in electric train ans how much volt.
How much duration I can keep open the CT if it is under loading condition(100 Amp load)?
3 Answers Infosys, NTPC, Suzlon,
What is HT? And specify the range of voltage?
Why voltge arev transformed in to 132KV/66/KV/33KV like that
Why the suply frequency in INDIA is 50HZ
How we calculate the size of H.T cable for any transformer & rating of busbar for any L.T. panel?
Explain why the Voltage drop will happen in 3 Phase line?
I have carried out wiring for lighting in a shed in Industrial area which contains Metal halide lamps & have balanced in 3ph.Now when we put all the lines on in the daytime the current taken at 3phases at MCB comes to be equal i.e.28,29,28Amps respectively but in the night time i.e between 7p.m.to 11p.m. at the same MCb the current is 52,59,62Amp, though I have fit 63A MCB it is tripping in the above period.What may be the reason.? Note: This industry is located in industrial area where majority of steel ingot manufacturing plants are there. Whether this may be due to harmonic? what should I do to overcome above problem.pl suggest urgently.
how to select fuse in any circuit? if with fomula ?and examples also
can v use earth as nutral. yes than y.if not y.
what is the wattage of 'zero watt' bulb?