Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


i have 28/32 MVA power transformer with 11/6.6 KC voltage
rating and 12%impedance.it have star connection at both
side.but it have another thied winding tertiary
winding.what is used of this winding.

pl tell me

Answers were Sorted based on User's Feedback



i have 28/32 MVA power transformer with 11/6.6 KC voltage rating and 12%impedance.it have star con..

Answer / manish meena

tertiary winding used for,
-to obtain additional voltage
-to stabilize neutral in case of star/star transformer
-to reduce third harmonics and control zero sequence
impedance.

Is This Answer Correct ?    6 Yes 1 No

i have 28/32 MVA power transformer with 11/6.6 KC voltage rating and 12%impedance.it have star con..

Answer / vipin

its for eliminating the harmonics

Is This Answer Correct ?    4 Yes 1 No

i have 28/32 MVA power transformer with 11/6.6 KC voltage rating and 12%impedance.it have star con..

Answer / jnanesh

In star connected trans. third hormonics is significant so
to reduce that effect it is used.In delta connected trans.
third hormonics circulate witin and there is no effect.
Also plz note that in some substation for feeding internal
power to substation or local area this additional winding
is used.

Is This Answer Correct ?    3 Yes 0 No

i have 28/32 MVA power transformer with 11/6.6 KC voltage rating and 12%impedance.it have star con..

Answer / sunil

it is used for reducing third harmonics currents

Is This Answer Correct ?    3 Yes 1 No

i have 28/32 MVA power transformer with 11/6.6 KC voltage rating and 12%impedance.it have star con..

Answer / ajay patel

How your tertiary Winding is connected? what is the rating?
If all three phase terminals are bruoght out then it can be
used as additional seondary winding. But If this tertiary
is connected in Open Delta & 2 termianls of open delta
brought our for Earthing. That means this is installed for
Harmonic purpose. If you have rectifier, Big VFDs or such
load which can generate Theird Harmonic in big amount then
these third harmonic can be reflected in entire Grid, if
your transformer is Star - Star. Which is may damage other
equipments / consumers also who are connected with same
supply. Hence it is necessory to control 3rd harmonics in
grid. For this you can provide Delta Primary for
Transformer. But you dont have delta in primay tehn you
have to provide Tertiary winding with open Delta. This Open
delta is closed out side of Transformer & Complete Delta is
formed. This Delta winding should be earthed to minimise
harmonic disturbance in the system. Please check, do you
have earthed tertiary? Is it in Delta?

Is This Answer Correct ?    2 Yes 0 No

i have 28/32 MVA power transformer with 11/6.6 KC voltage rating and 12%impedance.it have star con..

Answer / manish jauhari

Any unbalanced loads, results in increased cirulating
current with in tertiary Delta winding, thereby keepinng
pri & sec voltages with in limits.

Is This Answer Correct ?    2 Yes 2 No

i have 28/32 MVA power transformer with 11/6.6 KC voltage rating and 12%impedance.it have star con..

Answer / engr. l. o. osuji

Hi Paliwalsureshi,
Makers of such transformers usually provide a tertiary
winding connected in delta. This winding is sometimes called
compensating winding. As others have rightly said this
winding help to eliminate the harmoics which may interfer
with communication in power system. Before the advent of
microprocessor-based differential relays the old
differential scheme with star-star on one must have a delta
winging in between.In a nutshell any star-star connection
must have a delta tertiary.

Is This Answer Correct ?    0 Yes 1 No

Post New Answer

More Electrical Engineering Interview Questions

difference between generator and alternator

0 Answers   Havells,


what is the practical application of full adder circuit?

0 Answers   College School Exams Tests,


Will MCB tripped off, if there is an electric shock to Human body?

9 Answers  


I PURCHASED A DEISEL GENARATOR SET OF AVR TYPE& RATING 125KVA BUT SOME TIMES THE OUTPUT VOLTAGE IS FLUCTUATING WHAT ARE THE PROBABLE REASONS GIVE ME

0 Answers  


What do you mean by Stimulastion Test in Diesel Genarator / Why & when it's conducted ?

0 Answers   JLL,


What is K-rated transformer? What is the use of it? What can be the size(pls provide calculation if possible) of K- factor transformer for 550kW,690V motor operating with drive (VFD)?

0 Answers  


What is cable tray, its type, and its support?

0 Answers  


how to test an MCB

2 Answers  


why the conservater tank alwes made upper side of transformer???

3 Answers  


what do you mean by puncturing of insulator by ice -coating?

2 Answers  


If we are importing real power & exporting reactive power then what will be the effect on our system

3 Answers  


what is the speed of current?

29 Answers   Su Kam, TATA,


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)