We order Dyn 5 distribution transformer to a company. What arrives is Dyn 11. Is it ok to use this transformer.
It will be installed alone.
Answers were Sorted based on User's Feedback
Answer / bheesham acharya
Dyn11 and Dyn5 both are vector Group b/w phases and neutral....
D is indicate Primary side Delta connection,
y is indicate secondary side Star connection,
N is indicate Neutral and
5 and 11 is just indicate the angle
5 is show 30 degree angle and 11 is show 120 degree angle b/w star phase and in neutral connection
Is This Answer Correct ? | 0 Yes | 0 No |
Can I parallel 1 MVA generator with 1kVA Generator? if V, F, Ph Seq and Ph angles are same
In a power system we know that if the generated power is less than the load then the frequency of the system is decreases.So does this mean that total required load is delivered at alower frequency?
Why 11kv to be generated in generation station
0 Answers TNEB Tamil Nadu Electricity Board,
i want to run 11kv star connected motor in 6.6kv with delta connected throught inverter, is it possible?
If a ACB breaker is tripping and closing problem, then what will we check internal..?
What is VCB? where it is installed at SP. What is SP?
ell me capacitor bank chossen formula.load in KW
whats is the role of power factor in designing a tariff structure?
which types of tests are required after commissioning of 6.6 kva tranformer?
how do u get less voltage in star connection
every motors written in name plate IP 55 what is this?
dc supply given to dc generator winding.how is possible? my knowledge is saying the winding will burn. please reply.