WHAT ARE THE FACTORS REQUIRED FOR SELECTION OF TRANSFORMER
RATING?
Answers were Sorted based on User's Feedback
Answer / kannan.sj
first u should know
1,The connected load of transformer or load factor
2,Highest connected load / motor in the transformer and its
starting type
3, diversity factor
because
KVA demand at 0.8 p.f =connected load x LF x DF
-------------
efficiency X p.f
starting current of highest KW load takes 6 times of full
load current. so we to check it whether the transformer has
the capability to feed the load or not during starting. its
the important thing while considering trafo selection..
| Is This Answer Correct ? | 57 Yes | 6 No |
Answer / guest
You need to know the load type and calcuation of schort
circuit
| Is This Answer Correct ? | 25 Yes | 14 No |
Answer / ahfaz
1] we have to know the KVA load required
2] we have to know the percentage of impedance in the winding
3] Indoor or Outdoor
4] Type of cooling
5] Maximum temperature required
Thanks & regards
Ahfaz
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / shaista
SECONDARY LOAD VOLTAGE
KVA Rating
application of use
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / mohammed hussain a
Load Current,Load Voltage and Load Power factor(Secondary
Side). It may 3 Phase or 1Phase.
For 3phase Power in KVA = 1.732*V*I/0.8*1000
For 1 Phase in KVA = V*I/1000.
The rating of the transformer can be identified from the
above formula.
| Is This Answer Correct ? | 13 Yes | 11 No |
Answer / mgm
calculate all connected load like lighting load power load
motors ahu etc, calculate the 3 phase current and multiply
it with 1.25%
we will get the transformer size
| Is This Answer Correct ? | 1 Yes | 1 No |
Answer / manasa
First we have to know about the load consumption, then
diversity factor that is demand in KW and then in KVA
| Is This Answer Correct ? | 7 Yes | 10 No |
what is the generator rating for 40 amp load of 3phase motor.?? 400v voltage of generator... plz tell me with formula its urgent...plzzz... and also tell me that this 40 amp at all phases mean 40 amp on red,40 amp on yellow,40 amp on blue...... or the total sum of that 3phase is 40 amp....
What happened If 3phase supply connected to slip ring side of slipring induction motor ?
ADVANTAGES OF DIGITAL COMMUNICATION OVER ANALOG.?
How much depth we will take in 33kv sub station and why.
how to calculate the capacity of the AC motor
We use MCCB not MCB for motor starters because MCCBs has capablity to drawout the motor starting current which is 5-6 times the full load current of motor for 1sec. Then why we use SDF in starter panel means MCC panels. Pls reply if any one knows this answer.
In hydel power plants, L.A's, S.C's are placed inside the control panel boards. what is the purpose? [already the total body was earthed to ground.]
Which colour of earthing wire
Generator,motor and alternator Working principal Please explain easily
What is meant by full pitched winding?
If we impress a dc voltage of 230 V on an unloaded 230 V, 50 Hz transformer it wi A give high secondary voltage B burn out C give secondary voltage as per K D none of these
what is mean by marshalling box in transformer?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)