Answer / kannan.sj
first u should know
1,The connected load of transformer or load factor
2,Highest connected load / motor in the transformer and its
starting type
3, diversity factor
because
KVA demand at 0.8 p.f =connected load x LF x DF
-------------
efficiency X p.f
starting current of highest KW load takes 6 times of full
load current. so we to check it whether the transformer has
the capability to feed the load or not during starting. its
the important thing while considering trafo selection..
| Is This Answer Correct ? | 57 Yes | 6 No |
Answer / guest
You need to know the load type and calcuation of schort
circuit
| Is This Answer Correct ? | 25 Yes | 14 No |
Answer / ahfaz
1] we have to know the KVA load required
2] we have to know the percentage of impedance in the winding
3] Indoor or Outdoor
4] Type of cooling
5] Maximum temperature required
Thanks & regards
Ahfaz
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / shaista
SECONDARY LOAD VOLTAGE
KVA Rating
application of use
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / mohammed hussain a
Load Current,Load Voltage and Load Power factor(Secondary
Side). It may 3 Phase or 1Phase.
For 3phase Power in KVA = 1.732*V*I/0.8*1000
For 1 Phase in KVA = V*I/1000.
The rating of the transformer can be identified from the
above formula.
| Is This Answer Correct ? | 13 Yes | 11 No |
Answer / mgm
calculate all connected load like lighting load power load
motors ahu etc, calculate the 3 phase current and multiply
it with 1.25%
we will get the transformer size
| Is This Answer Correct ? | 1 Yes | 1 No |
Answer / manasa
First we have to know about the load consumption, then
diversity factor that is demand in KW and then in KVA
| Is This Answer Correct ? | 7 Yes | 10 No |
IS HI-POT TEST DONE ON A TRANSFORMER - YES OR NO? WHY?
if we convert ampers into kwh or mwh ,which one formula use by us,pls tell me?
what is zinc diffusion?
what will happen if delta - star , 400V to 6.6KV step up transformer neutral is not grounded, Neutral is not used but transformer is provided with neutral.
If my sfu is 64 Amp & its link is 32 Amp then at what amp.my sfu will trip???
what is the difference between brush & brushless dc motor explain its operation ?
what is the difference between neutral and earth?
is there any chart showing the suitable cable size according to AMP and length ? for three phase motors
What is a circuit breaker contact multiplier relay?
what happens in the short circuited secondary transformer,if the resistance of the short circuit is increased gradually?
what is working parincipal of a ht transformer
what shall be no load voltage of 132/33 kV transformer ? is it 33 kv of 34.5 kV
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)