WHAT ARE THE FACTORS REQUIRED FOR SELECTION OF TRANSFORMER
RATING?

Answers were Sorted based on User's Feedback



WHAT ARE THE FACTORS REQUIRED FOR SELECTION OF TRANSFORMER RATING?..

Answer / kannan.sj

first u should know
1,The connected load of transformer or load factor
2,Highest connected load / motor in the transformer and its
starting type
3, diversity factor
because
KVA demand at 0.8 p.f =connected load x LF x DF
-------------
efficiency X p.f
starting current of highest KW load takes 6 times of full
load current. so we to check it whether the transformer has
the capability to feed the load or not during starting. its
the important thing while considering trafo selection..

Is This Answer Correct ?    57 Yes 6 No

WHAT ARE THE FACTORS REQUIRED FOR SELECTION OF TRANSFORMER RATING?..

Answer / satyam

VOLTAGE & CURRENT

Is This Answer Correct ?    26 Yes 14 No

WHAT ARE THE FACTORS REQUIRED FOR SELECTION OF TRANSFORMER RATING?..

Answer / guest

You need to know the load type and calcuation of schort
circuit

Is This Answer Correct ?    25 Yes 14 No

WHAT ARE THE FACTORS REQUIRED FOR SELECTION OF TRANSFORMER RATING?..

Answer / ravi k lavu

Total connected load of plant

Is This Answer Correct ?    21 Yes 10 No

WHAT ARE THE FACTORS REQUIRED FOR SELECTION OF TRANSFORMER RATING?..

Answer / ahfaz

1] we have to know the KVA load required
2] we have to know the percentage of impedance in the winding
3] Indoor or Outdoor
4] Type of cooling
5] Maximum temperature required

Thanks & regards

Ahfaz

Is This Answer Correct ?    3 Yes 0 No

WHAT ARE THE FACTORS REQUIRED FOR SELECTION OF TRANSFORMER RATING?..

Answer / shaista

SECONDARY LOAD VOLTAGE
KVA Rating
application of use

Is This Answer Correct ?    3 Yes 0 No

WHAT ARE THE FACTORS REQUIRED FOR SELECTION OF TRANSFORMER RATING?..

Answer / mohammed hussain a

Load Current,Load Voltage and Load Power factor(Secondary
Side). It may 3 Phase or 1Phase.

For 3phase Power in KVA = 1.732*V*I/0.8*1000

For 1 Phase in KVA = V*I/1000.

The rating of the transformer can be identified from the
above formula.

Is This Answer Correct ?    13 Yes 11 No

WHAT ARE THE FACTORS REQUIRED FOR SELECTION OF TRANSFORMER RATING?..

Answer / mgm

calculate all connected load like lighting load power load
motors ahu etc, calculate the 3 phase current and multiply
it with 1.25%
we will get the transformer size

Is This Answer Correct ?    1 Yes 1 No

WHAT ARE THE FACTORS REQUIRED FOR SELECTION OF TRANSFORMER RATING?..

Answer / dinesh kumar

1.Load factor
2.Diversity Factor

Is This Answer Correct ?    10 Yes 12 No

WHAT ARE THE FACTORS REQUIRED FOR SELECTION OF TRANSFORMER RATING?..

Answer / manasa

First we have to know about the load consumption, then
diversity factor that is demand in KW and then in KVA

Is This Answer Correct ?    7 Yes 10 No

Post New Answer

More Electrical Engineering Interview Questions

in a delta-star with neutral grounding on star side what will happen if one star limb  got opened at star point

1 Answers   NTPC,


why we ground the scondary of current transformer.

4 Answers  


avr is an automayic voltage regulator ... it regulates voltage before it synchronise with grid after synchronisation it regulates power factor why....

7 Answers  


What are the difference between these terms ? e.m.f, voltage, potential, potential difference, current etc? what are the difference between these terms ? (electromotive force) e.m.f, voltage, potential, potential difference, reference potential, reference potential difference, current. How can i explain and describe these all terms in single line each and little more explaination too thanks

2 Answers   Siemens,


THE ROTIO OF VOLTAGE AND CURRENT IN A CLOSED CIRCUIT

12 Answers   APGenco, Constant, Lanco,






Why 3 phase induction motor getting supply in body if one of it's phase is cut

0 Answers  


which one has maximum efficiency autotransformer or transformer?? and why??

2 Answers  


why phase to phase voltage is 400v while phase to neutral is 220v?

1 Answers  


Why? We r used 50sq. mm. And above size cable in 3.5 core and below size are used in 4core

2 Answers  


we have 400kv/6.6kv transformer ,it has total 9 taps on HV side with normal tap on tap no 5.when we took the ratio test we observed that ratio was decreasing from tap 1 to tap 5 and was found increasing from tap 5 to tap 9.What is the reason?if anyone have related document then please send me on the email id ankushbahale@gmail.com......plz plz

1 Answers  


application s to shunt coil

0 Answers  


what is tandem isolator ??????????

5 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4452)
  • Electrical Engineering Interview Questions Electrical Engineering (16637)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)