Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


How will you calaculate the Ct ratio based on connected
load 500KVA,and 11KV supply ?

Answers were Sorted based on User's Feedback



How will you calaculate the Ct ratio based on connected load 500KVA,and 11KV supply ?..

Answer / venu

p=root3*v*i
500K=root3*11K*I
hence we get
I=62.096
so this is the maximum current flowing to the particular
load so we can use 75/1A ratio CT

Is This Answer Correct ?    19 Yes 9 No

How will you calaculate the Ct ratio based on connected load 500KVA,and 11KV supply ?..

Answer / bala.a

first u shouls convert to A
500 / (root 3 x 11 )= 26.2A
So u can select 50/1A CT FOR THE ABOVE LOAD

Is This Answer Correct ?    8 Yes 1 No

How will you calaculate the Ct ratio based on connected load 500KVA,and 11KV supply ?..

Answer / pkv

50/5 or 50/5 depending upon the protection relay amp

Is This Answer Correct ?    3 Yes 1 No

Post New Answer

More Electrical Engineering Interview Questions

Can we use both Electrical & mechanical interlock between tow breakers? if yes how, please explain

0 Answers  


what is the ideal earth resistance

11 Answers   Amit Enterprises, Enercon,


What are the components of feedback control system?

0 Answers  


why Square root 3 used for three phase?

2 Answers  


What is Transformer?

23 Answers   HSL,


Which type of power plant is more easier to produce electrical power at economical condition?

5 Answers   HAL,


How can claculate to attain the desired PF in the line ( HOW Much KVAR is required ) Pls Give the formula? Equate Petrochemical 0 1 how to calculate sizing of NGTR (Transformer rating,Loading resistor value and Current rating of resistor) and what is the X/R ratio. Details : 11kV,Capacitance 1.73532 micro farads,40kA for 1sec. 0 1 What will happened. if we feed 3phase supplay to the stater with out insert the rotor. How much current will flow through the stater winnding? Equate Petrochemical 0 1 What is required of exietation to the alternater. 0 1 why star point of HT motor not earthed? Equate Petrochemical 0 1 Why we are getting low voltage in star connection? Equate Petrochemical 0 2 What's ND relay & it's functions? Equate Petrochemical 0 2 How instantanious short circuit current is calculated? its formula? Equate Petrochemical 0 2 What is servo Motor? What's the advantages of this motor over Induction motor? Equate Petrochemical 0 2 What is core CT & it's function? Equate Petrochemical 0 3 what is meant by star/delta voltages as 440/220 in a 3 phase induction motor, and why it should be connected on STAR IN 3 PHASE SUPPLY L & T 0 4 What is required of exietation to the alternater. KNB 1 23 what is the design voltage for 6.6KV 2000 KVAR HT capacitor? Consultancy 0 3 Pls explain about vfd control?Where it is used, Give some example? siemens 1 22 Please explain me abt PQ diagaram in the power sector. 0 9

0 Answers  


If there is no problem with the electronic circuit and regulator then why the motor start rotating at low value of regulator with full speed both at laod and no load??? and if my judgement of circuit is wrong then what is your openion?

1 Answers  


acsr dog conductor specification

1 Answers  


for hipot test on 33kV busbar, we will test on 70 kV or 56kV, what is the acceptable leackage current?

0 Answers  


If the (Motor control center)Panel work on field the relay used in panel in the case this will be damage and no indication provide on panel.fault occur in panel and MCB will not trip. how happen the relay damage in panel and what effect of panel.

1 Answers  


As per the Anchor capstan motor specification, full load current is 200A. starting current is 1750 A and acceleration time is less than 8 seconds. Please guide for selection of cable size.

0 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4453)
  • Electrical Engineering Interview Questions Electrical Engineering (16638)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)