Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


How do we check transformer losses and what are the ways to
minimise it.

Answers were Sorted based on User's Feedback



How do we check transformer losses and what are the ways to minimise it...

Answer / guest

transformer losses can be found by doing open circuit test
and short circuit test
open circuit test gives the core losses
short circuit test gives the copper losses
note in open circuit test the lv side is given supply and
in short circuit test the hv side is given supply

the iron losses can be reduced by providing laminations of
thinner dimension and using c.r.g.o sheet for laminations

the copper losses depend on the winding resistance which
increases due to heat can be reduced by providing
sufficient cooling to the winding.

Is This Answer Correct ?    36 Yes 2 No

How do we check transformer losses and what are the ways to minimise it...

Answer / manthesh.patil

we can check transformer losses by short ckt and open ckt test
,for checking cu loss we use short ckt test and for iron
loss we use open ckt test..to reduce copper loss we should
go for good cooling and for iron loss the core should be
perfectly laminated

Is This Answer Correct ?    26 Yes 4 No

How do we check transformer losses and what are the ways to minimise it...

Answer / sumitgarg

we can check a trans losses by open circuit and short
sircuit test.
to minimise these losses we shuold have a good cooling
system. apart from that all other points are related with
the insulation of the core,permitivity etc.

Is This Answer Correct ?    27 Yes 10 No

How do we check transformer losses and what are the ways to minimise it...

Answer / achala.g.s.

We can check like the following :
polarity, resistance and tap change operation tests should me made to check whether it has built correctly or not..


the ways to minimize it are:
*check of Oil quality.
*A check on the tap changer.

Is This Answer Correct ?    3 Yes 1 No

How do we check transformer losses and what are the ways to minimise it...

Answer / saravanan

oc and sc test helps to find the total losses means .oc test
gives the core loss .sc test gives the copper loss.if the
transformer is oil cooled means you must check the
conduction or breakdown test on the transformer oil. that
time only we can suggest the winding insulation loss

Is This Answer Correct ?    2 Yes 7 No

Post New Answer

More Electrical Engineering Interview Questions

Why 15Amp. MCB is suitable to carry load of 1.5Ton Ac please Explain?

0 Answers  


if a 2 ohm resistor,2 ohm capacitor and a 2 ohm inductor is connected parallely to 12v source.Then what is the value of current in each branch.Is current flows in each branch at the same time?If not so then provide the proper sequence

1 Answers   Tata Steel Limited,


in india are trains run by DC or AC? if DC , from where it receives negative potential? because pentograph receives singe potential only?

2 Answers   GATE, PSU,


I am getting above 60 V as open delta voltage against single phase unit ICT at tertiary delta formed and ICT getting trippped on NDR. ICT tested and found in order. PTs provided on tertiary are tested and in order. what may be the reason?

0 Answers  


What is the working principle of ceiling fan?

6 Answers   Indian Navy,


what is the difference between skin effect

0 Answers  


How is earthing done in Aerospace applications such as Flights and spaceships..?

1 Answers  


What is auto reclose system in Circuit breakers

1 Answers  


Is a contactor (or master relay) required between incoming lines and a VFD? The question goes to safety. If a contactor were used before the VFD and an e-stop engaged then the motor will coast to a stop (i.e. VFD loses power) instead of stopping much faster if the VFD braking fucntion were used. It would make more sense to keep power on the VFD.

0 Answers   Pride Hotels,


What is percent age of scrap of wires as per IE Rule Clause No in wiring for House and Industrial wiring ?

3 Answers  


What is induction motor

1 Answers   Indoco Remedies,


why the neutral of power transformer is always earthed?

1 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)