How do we check transformer losses and what are the ways to
minimise it.
Answers were Sorted based on User's Feedback
Answer / guest
transformer losses can be found by doing open circuit test
and short circuit test
open circuit test gives the core losses
short circuit test gives the copper losses
note in open circuit test the lv side is given supply and
in short circuit test the hv side is given supply
the iron losses can be reduced by providing laminations of
thinner dimension and using c.r.g.o sheet for laminations
the copper losses depend on the winding resistance which
increases due to heat can be reduced by providing
sufficient cooling to the winding.
Is This Answer Correct ? | 36 Yes | 2 No |
Answer / manthesh.patil
we can check transformer losses by short ckt and open ckt test
,for checking cu loss we use short ckt test and for iron
loss we use open ckt test..to reduce copper loss we should
go for good cooling and for iron loss the core should be
perfectly laminated
Is This Answer Correct ? | 26 Yes | 4 No |
Answer / sumitgarg
we can check a trans losses by open circuit and short
sircuit test.
to minimise these losses we shuold have a good cooling
system. apart from that all other points are related with
the insulation of the core,permitivity etc.
Is This Answer Correct ? | 27 Yes | 10 No |
Answer / achala.g.s.
We can check like the following :
polarity, resistance and tap change operation tests should me made to check whether it has built correctly or not..
the ways to minimize it are:
*check of Oil quality.
*A check on the tap changer.
Is This Answer Correct ? | 3 Yes | 1 No |
Answer / saravanan
oc and sc test helps to find the total losses means .oc test
gives the core loss .sc test gives the copper loss.if the
transformer is oil cooled means you must check the
conduction or breakdown test on the transformer oil. that
time only we can suggest the winding insulation loss
Is This Answer Correct ? | 2 Yes | 7 No |
What are series and parallel isolators?
how much kn lightning arrestor is used in 11kv line
what is power factor
HOW TO CALCULATE THE HEAT AND LOAD OF LT-SUBSTATION WHICH CONTAINS 2*1MVA TRANSFORMERS,LT SWITCH BOARD,MLDB,ACB,BUSBAR,ETC...?
write encoder 17 pins details? pin a;b+, pin b;w+,..pin s & t. what is the meaning of b+, w+? explain;
What happen if LV supply is fed to a HT motor?
19 Answers ITC Infotech, Jindal,
What does the term supermesh means?
Do power transformers have an Automatic Voltage Regulator (AVR) just like the alternator/generator in a power system?
what is the effect come when i changed the alternator exciter field winding DC palority(+ve & -ve)which is coming from AVR.
why the capacitor bank unit is kvar
what maximum load will take a aluminum cable of 50mm 4 core.
Why synchronous motor runs at a fixed speed? what is the name of that fixed speed?