How can we calculate the fault level of the distribution
system knowing the percentage impedance of transformer &
subsequent equipments.
Answers were Sorted based on User's Feedback
Answer / mbao richie
simply means the bus rated at that fault level can
withstand the electrical pressure(voltage) for which it is
designated for that period of time
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / srikanth
Dear friends,
in the above calculations people consider the % impedence
but they are not calculate the fault impedence to get MVA
of transformer.
| Is This Answer Correct ? | 0 Yes | 1 No |
Answer / jigar shah
suppose transformer (11 KV/433) is of 1000 KVA & %
impedance is 4 .LT side Fault level can be calculated as
below :
KVA = 1.732 X V X I X Cos Phi - PF assumed : 0.95
LT Rated current (I) = (1000 * 1000)/(1.732*433*0.95)
= 1481 A
Fault current on LT side = FLC * 100/(% impedance)
= 1481 * 100/5
= 29.62 KA
| Is This Answer Correct ? | 44 Yes | 54 No |
Answer / laxminarayan
suppose transformer (11 KV/433) is of 1000 KVA & %
impedance is 4 .LT side Fault level can be calculated as
below :
KVA = 1.732 X V X I X Cos Phi - PF assumed : 0.95
LT Rated current (I) = (1000 * 1000)/(1.732*433*0.95)
= 1481 A
Fault current on LT side = FLC * 100/(% impedance)
= 1481 * 100/5
= 29.62 KA
| Is This Answer Correct ? | 14 Yes | 46 No |
How Calculat the Cable Sizing of HT/LT System & Explian by one Exampal?
How would we calculate the no of earthing pits required for motor /panel
5 Answers APGenco, National Engineering Industries, Practical Viva Questions,
What do you understand by external characteristics of a d.c. Generator?
What happen if we have run 415 V,50Hz designed motor at on 480V,60HZ
What happen if the 24 volt DC supply is disconnected from air circuit breake ?
explain supply side and demand side energy management with advantages & disadvantages
is it possible to flow currnet between earth and nutral wire in a circuit???
what different in delta & star connection in motor?explain
5 Answers Bhushan Power Steel, Hyundai, KPCL, L&T,
What is the make of breakers, transformers, generators? What are their capacities and ratings?
what is magnetizing current test in power transformer
why florescent light was flickering?
what is the string efficiency
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)