How can we calculate the fault level of the distribution
system knowing the percentage impedance of transformer &
subsequent equipments.
Answers were Sorted based on User's Feedback
Answer / mbao richie
simply means the bus rated at that fault level can
withstand the electrical pressure(voltage) for which it is
designated for that period of time
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / srikanth
Dear friends,
in the above calculations people consider the % impedence
but they are not calculate the fault impedence to get MVA
of transformer.
Is This Answer Correct ? | 0 Yes | 1 No |
Answer / jigar shah
suppose transformer (11 KV/433) is of 1000 KVA & %
impedance is 4 .LT side Fault level can be calculated as
below :
KVA = 1.732 X V X I X Cos Phi - PF assumed : 0.95
LT Rated current (I) = (1000 * 1000)/(1.732*433*0.95)
= 1481 A
Fault current on LT side = FLC * 100/(% impedance)
= 1481 * 100/5
= 29.62 KA
Is This Answer Correct ? | 44 Yes | 54 No |
Answer / laxminarayan
suppose transformer (11 KV/433) is of 1000 KVA & %
impedance is 4 .LT side Fault level can be calculated as
below :
KVA = 1.732 X V X I X Cos Phi - PF assumed : 0.95
LT Rated current (I) = (1000 * 1000)/(1.732*433*0.95)
= 1481 A
Fault current on LT side = FLC * 100/(% impedance)
= 1481 * 100/5
= 29.62 KA
Is This Answer Correct ? | 14 Yes | 46 No |
After synchronization with grid what is the demand value QKVAR and how we will maintain that?
What are the various kind of cables used for transmission?
solar energy light efficiency & disadvantages?
What happens to the synchronous generator when reverse power is given to it?
How many types of oil using in H/T & L/T Oil Circuit Breakers. need Explenation ?
Can you explain about Restricited earth fault protection scheme
how to calculate the no. of earth pits required for an electrical installation?
What are eddy current and define rms value?
What is R/X ratio? I have heard that this ratio is higher in a radial distribution system.Why is it so? I would appreciate a word. Thank you
1 Answers Power Grid, Vignan University,
why indicated sypply only by 440V in 3-phase system.
If the field winding of the dc shunt motor is removed then what will happen to the motor ? will it turn or not
Explain The Application Of Storage Batteries?