Answer / mbao richie
simply means the bus rated at that fault level can
withstand the electrical pressure(voltage) for which it is
designated for that period of time
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / srikanth
Dear friends,
in the above calculations people consider the % impedence
but they are not calculate the fault impedence to get MVA
of transformer.
| Is This Answer Correct ? | 0 Yes | 1 No |
Answer / jigar shah
suppose transformer (11 KV/433) is of 1000 KVA & %
impedance is 4 .LT side Fault level can be calculated as
below :
KVA = 1.732 X V X I X Cos Phi - PF assumed : 0.95
LT Rated current (I) = (1000 * 1000)/(1.732*433*0.95)
= 1481 A
Fault current on LT side = FLC * 100/(% impedance)
= 1481 * 100/5
= 29.62 KA
| Is This Answer Correct ? | 44 Yes | 54 No |
Answer / laxminarayan
suppose transformer (11 KV/433) is of 1000 KVA & %
impedance is 4 .LT side Fault level can be calculated as
below :
KVA = 1.732 X V X I X Cos Phi - PF assumed : 0.95
LT Rated current (I) = (1000 * 1000)/(1.732*433*0.95)
= 1481 A
Fault current on LT side = FLC * 100/(% impedance)
= 1481 * 100/5
= 29.62 KA
| Is This Answer Correct ? | 14 Yes | 46 No |
Is potential difference materials property ..? if yes tnen how.. explain brifly.
Between educational qualification and practical work experience, give us a brief explanation on your practical experience in your past Endeavour that you performed well to the satisfaction of your past or present employer?
what is the use of the circle diagram
1)what is hypo test. 2) which cable need to hypo test.3) when hypo test can be done before or after glanding.4) what is the purpose of hypo test.
Why motor initial starting current is high?
What will happen if the oil level in the buchholz realy of a transformer gets down?
How to design power source say 5KW i/p :415v 3 ph, o/p 5KW constant, variable currnt and variable volatge 10-230v,
How does the slip regulator works as a startor
i have a Connected Load of 280KW and Maximum Demand of 224KW to one of SMDB under design with me. which criteria should i consider to design panel and main cables connected Load or Maximum Demand 1)Breaker rating 2)Panel Busbar rating 2)Incommer cable sizing (ignore Voltage drop)
What is an Isolation Transformer? Where it will use?
which circuit breaker enclosure is best for maintenance guy? 16 bolt & 20 bolt squre or 16,20 bolt hinge
why a pilot exciter is used in combination with the main exciter? why not only a main exciter is used for excitation to an alternator?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)