What will happen if the oil level in the buchholz realy of
a transformer gets down?
Answers were Sorted based on User's Feedback
there are two levels,in the first level if the level of oil
is decreased then it sends an alarm signal to the
operator,if the operator ignores then the gas formation in
the bank of relay increases then he second level of
protection is activated as it isolates the transformer.by
formation of gas in chamber they test the gas and conforms
where actual fault occured
Is This Answer Correct ? | 7 Yes | 0 No |
Answer / ashoke
The buchholz relay will operate in high fault condition only
and there will be no primary alarm due to low oil lebel in
the primary stage of the fault and the X-mer in high risk
because the secondary switching will be depend upon the
quantity of gas formation .
Is This Answer Correct ? | 0 Yes | 1 No |
in a induction motor if we put capacitor across it will the power factor of the motor will improve? if yes how
Dear sir/mam Iwant complete details of Naintenence of 33kv/433v Transformer having 1250 KVa
what is the difference between Earth and neutral? and what is the difference between ground earthing and neutral earthing?
what is the meaning of DSL
how many types of accuracy class in ct? what is meaning of 5p20?
At what speed 1 HP motor can run an electric car of weighing 400 kg?
differtiate between energy consevation and energy efficiency..
Difference Between B Curve & C Curve in MCB.
explain about RTCC
what are the disadvantages in GIS over AIS
what is phase voltage and phase current what is line current and line phase
Stator of 3-phase IM has 3 slots per pole per phase, calculate number of stator pole pairs. A 1 B 6 C 2 D 3