i have a Connected Load of 280KW and Maximum Demand of
224KW to one of SMDB under design with me.
which criteria should i consider to design panel and main
cables connected Load or Maximum Demand
1)Breaker rating
2)Panel Busbar rating
2)Incommer cable sizing (ignore Voltage drop)
Answer / satyam
As the maximum demand is less than connected load ,you have
to choose rating of power equipments depending upon
connected load .
| Is This Answer Correct ? | 4 Yes | 1 No |
will a bulb glow connected to two phases of a delta connection?
what are transmission line parameters and transmission line constants?
WHAT IS THE FAULT WHEN 100HP TURBINE MOTOR TRIPS, LIST THE FAULTS AND ITS TRABULESHOOTING TIPS.. MY AUTO TARNSFORMER STARTER TRIPS
How Negative Phase Sequence Relay works in case of Synchronous Motor?
1. Synchronization is not required A. Thermal B.Hydel C.Wind D.Nuclear
2 Answers APGenco, Birla Power,
which element is neglected during fault calculation? a)resistance b)inductance c)capacitance d)reactance
what is stiffness factor
Why is the earth socket in an electrical plug outlet made thicker and lenghty?
What is the effect of positive feedback on stability of the system?
WHAT IS VFD,FUNCTION, PURPOSE,
Why glands not provided for XLPE cables
To attain a powerfactor more than .95, how much kvr should we use for 100 HP of current
4 Answers Bhel, Scooters India,
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)