1)what is hypo test. 2) which cable need to hypo test.3)
when hypo test can be done before or after glanding.4) what
is the purpose of hypo test.
Answers were Sorted based on User's Feedback
Answer / mukund
high potential test carried between line-line, line-
neurtal,line and neutral to graund on any control panelto
check insulation between live conductors and enclosure body
at hv like 1.5kv and onward depands on system voltage and
local standard, it is carried out also on control wiring too
e.g. from 300 to 600v it need 2.7kv test for 1 second and
2.4kv for 1 minuts,note when this test have to do test job
must disconnected from line voltage,it is most likely
megeer test, after testing it need to discharge tested line
to graund
| Is This Answer Correct ? | 37 Yes | 7 No |
Answer / shams
hypo test is mostly used when any new cable is used or any cable which is repaired like tertiary cable in transformer.it is used to test the leakage current.20kv to 100kv dc is applied through hypo device to the testing material then the hypo device shows us the leakage current of that material
| Is This Answer Correct ? | 29 Yes | 1 No |
Answer / k.prakashchandra
It is high potential test. It is done on HV cables
compulsorily.Testing after glanding is mandatory.With this
test, we may know the highest safe working voltage
| Is This Answer Correct ? | 24 Yes | 7 No |
Answer / sajid
t is high potential test. It is done on HV cables
compulsorily.Testing after glanding is mandatory.With this
test, we may know the highest safe working voltage
| Is This Answer Correct ? | 7 Yes | 1 No |
Answer / muthu
hypo test meas cable strengthness cable inside armour to conductor shot have checking armour inject voltage conductor earth will check leakage current MA Formula 2E+1 ,E=Voltage 80% voltage inject
| Is This Answer Correct ? | 0 Yes | 0 No |
why AC voltage source are generate as 50 Hz ?
Can I do body earthing of machine by using Cable armour or I have to run another GI wire for body earthing and how many wires I need to run. Is there any rule for this. eartnig
what is the meaning of 1250 KVA Trasformer
Why the substation measure in KV but not in the power ratings of transformer.
What is the formuala to calculate the rating of motor protection circuit breaker
what is vtg limit of earth and neutral at transformer side?
iam completed my DEEE in eillm university. can i get the c licence in tamilnadu its possible or not
what is the meaning of electrical maintenance?
3 Answers GE Healthcare, MAHINDRA,
a wire in which bulb is connected there is two terminal when one terminal is connected to phase than why the value of current shock in nutral terminal is max. or large??
How to do the meggering for a cable.
we have provided 30 nos. relay contacts in panel.I want to know how do we do the numbering for the relay contacts as per any applicable standards
How we calculate the size of H.T cable for any transformer & rating of busbar for any L.T. panel?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)