1)what is hypo test. 2) which cable need to hypo test.3)
when hypo test can be done before or after glanding.4) what
is the purpose of hypo test.
Answers were Sorted based on User's Feedback
Answer / mukund
high potential test carried between line-line, line-
neurtal,line and neutral to graund on any control panelto
check insulation between live conductors and enclosure body
at hv like 1.5kv and onward depands on system voltage and
local standard, it is carried out also on control wiring too
e.g. from 300 to 600v it need 2.7kv test for 1 second and
2.4kv for 1 minuts,note when this test have to do test job
must disconnected from line voltage,it is most likely
megeer test, after testing it need to discharge tested line
to graund
| Is This Answer Correct ? | 37 Yes | 7 No |
Answer / shams
hypo test is mostly used when any new cable is used or any cable which is repaired like tertiary cable in transformer.it is used to test the leakage current.20kv to 100kv dc is applied through hypo device to the testing material then the hypo device shows us the leakage current of that material
| Is This Answer Correct ? | 29 Yes | 1 No |
Answer / k.prakashchandra
It is high potential test. It is done on HV cables
compulsorily.Testing after glanding is mandatory.With this
test, we may know the highest safe working voltage
| Is This Answer Correct ? | 24 Yes | 7 No |
Answer / sajid
t is high potential test. It is done on HV cables
compulsorily.Testing after glanding is mandatory.With this
test, we may know the highest safe working voltage
| Is This Answer Correct ? | 7 Yes | 1 No |
Answer / muthu
hypo test meas cable strengthness cable inside armour to conductor shot have checking armour inject voltage conductor earth will check leakage current MA Formula 2E+1 ,E=Voltage 80% voltage inject
| Is This Answer Correct ? | 0 Yes | 0 No |
How Calculet The UPS AH In Load
During the main stator winding insulation testing (phase to ground)of 11kv alternator (Lerysomer) i found 0 and resistance with multimeter and found 20 killo ohm while the power cables are connected both end (Generator & VCB). In VCB PT (Potential transformer) are connected. Please any body explain that method of insulation is correct or not? also describe of PT connections
what is post close & pre close of trip circuit supervision relay in circuit breaker control scheme?
how can i determine the KVA/MVA rating of transformer precisely?? is there any standard test?????
why the impedence of the transformer is expressed in percentage?
what is the diffrence between capasitor and battery?
What is ignition module of a CAT Gas Genset G-3508 Engine, Alternator SR4B Series. HOw its checked for correct functioning.Is it repiarable or replacable?
How we select the cable rating
Can anyone send details regarding motor protection relays ? their manuals please ?
what is meant by lagging & leading current
We have 2 Nos. Transformer with the capacity of 2000KVA and 1250 KVA and currently using only one 2000KVA T/R during operational hours while non- operational hous 1250 KVA T/R also used to reduce T & D losses. Similarly, 2 capacitor bank of 500KVAR and 300 KVAR also installed to balance reactive power. Now problem is around 1000 KW load PF is not maintaning 0.99 as 350 KVAR capacitor is in healty condtion. Now the PF is maintain 0.95 to 0.96.
how to discharge 3 phase power factor correction capacitors
0 Answers M S Ramaiah Institute,
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)