1)what is hypo test. 2) which cable need to hypo test.3)
when hypo test can be done before or after glanding.4) what
is the purpose of hypo test.
Answers were Sorted based on User's Feedback
Answer / mukund
high potential test carried between line-line, line-
neurtal,line and neutral to graund on any control panelto
check insulation between live conductors and enclosure body
at hv like 1.5kv and onward depands on system voltage and
local standard, it is carried out also on control wiring too
e.g. from 300 to 600v it need 2.7kv test for 1 second and
2.4kv for 1 minuts,note when this test have to do test job
must disconnected from line voltage,it is most likely
megeer test, after testing it need to discharge tested line
to graund
Is This Answer Correct ? | 37 Yes | 7 No |
Answer / shams
hypo test is mostly used when any new cable is used or any cable which is repaired like tertiary cable in transformer.it is used to test the leakage current.20kv to 100kv dc is applied through hypo device to the testing material then the hypo device shows us the leakage current of that material
Is This Answer Correct ? | 29 Yes | 1 No |
Answer / k.prakashchandra
It is high potential test. It is done on HV cables
compulsorily.Testing after glanding is mandatory.With this
test, we may know the highest safe working voltage
Is This Answer Correct ? | 24 Yes | 7 No |
Answer / sajid
t is high potential test. It is done on HV cables
compulsorily.Testing after glanding is mandatory.With this
test, we may know the highest safe working voltage
Is This Answer Correct ? | 7 Yes | 1 No |
Answer / muthu
hypo test meas cable strengthness cable inside armour to conductor shot have checking armour inject voltage conductor earth will check leakage current MA Formula 2E+1 ,E=Voltage 80% voltage inject
Is This Answer Correct ? | 0 Yes | 0 No |
why current coil has less number of turns compared to pressure coil?
What is the use of 1:1 isolation t/f in any circuit...?
why we use stones or rock pieces in transformer area?
how we can calculate power factor without knowing current in 230v 100w load ?
what is the function of choke in tube
What is the difference between a Vacuum Circuit Breaker and a Load Break Switch?
How to protect the water pump by no load running.
I got shortlisted in RRB thiruvananthapuram for the post of Junior Electrical engineer, waiting List - 7. i want to know about the validity of the current list and chance to get the job please help anybody knws abt it,, thank you
An 8 pole, 50 Hz, 3-phase IM is loaded to a poing where pull out torque will occur. The rotor resistance per phase is 0.3 ohm and motor stalls at 650 rpm. The rotor frequency at maximum torque point is A 3.33% B 4.44% C 5.55% D 6.66%
phase clearance between phase to phase and earth
what is %impedanece
how to calculate the current carring capacity of the conductor