Answer / nithi
This is to discriminate the wire-break of sensor and the
zero value of measured parameter.
ex:If pressure transducer measures 0 bar pressure,it will
send 4mA signal to the monitoring unit(EX:PLC).in case ,if
there is any break(dis-continuity) in wire then PLC senses
the 0 mA and gives alarm or shutdown depends on the
important of that parameter.
| Is This Answer Correct ? | 4 Yes | 0 No |
Answer / ind/elec
4-20 ma is used as opposed to 0-20 ma as at 0 ma this could
because of a break in cable or loss of supply and so
control would be ineffective.
| Is This Answer Correct ? | 2 Yes | 6 No |
what is skin effect and why is it absent in DC systems
List few applications of d.c series motor?
How to calculate ht side cable of 630 kva oil cooled outdoor transformer?
What is BUCKBOOST TRANSFORMER and Operation of Buckboost transformer?
What are the functions of different probes used in cro?
Hi, I've just got into my electrical engineering course and I need some help with a question of mine here. During a site visit, we were shown a main LT panel which has switchgears, ammeters and different kinds of relays and the distribution network from that panel. In the main LT panel I've noted down the current readings as Ir - 163A, Iy - 150A and Ib - 147A. The Line to Line voltage is 415 V at 50 Hz and Line to Neutral voltage is 230V at 50 Hz. From the above details, how would I calculate the kVA rating of transformer? The primary side voltage of the transformer is 11 kV and the secondary side voltage is 415V and the frequency is 50 Hz.
what is inverter and converter
0 Answers Hindustan Syringes and Medical Devices,
How we connect capacitors in Fixed Series compensation of AC transmission lines. Whether in parallel or in series?
Why computer humming sound occurred in ht transmission line?
Can anyone please provide me details of MCCB/Contactor/SFU rating calculations for a motor feeder..for example 50 kw.. not from type-2 cordination chart. i want manual calculations..
Define non-touching loop.
Advantage of LT panel vs HT panel ?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)