Which power will flow first if we switch on a motor? Active or
Reactive? How?
Answers were Sorted based on User's Feedback
reactive . Motor is an inductive load current lags the voltage .the product of +ve voltage and -ve current initially gives -ve power (i.e) reactive power.
| Is This Answer Correct ? | 22 Yes | 1 No |
Answer / rishi
reactive power will flow first because as we have generally the motor electrical equivalent circuit composed of series resistors and inductance.
now if in any such circuit if current is to flow then it must charge the inductors first and then current will flow through resistors. hence this will lead to reactive power flow at the very first instant of machine switching.
| Is This Answer Correct ? | 5 Yes | 1 No |
W and VAr are components of VA ,hence both may be co-incidental
| Is This Answer Correct ? | 2 Yes | 2 No |
Answer / dinesh ku mahanandia
reactive power flow first becouse reactive power start
flowing after the motor is switche on.
| Is This Answer Correct ? | 0 Yes | 0 No |
what is the principle of operation of synchronous motor and generator? explain in detail.
what happen when ac motor is connected with dc current
why there is no grow of grass under the high voltage transmission line?
what is the safe meggar values for motor, transformer HT, LT and Cables? IF we want to replace I/C bay at our 220 kv substation which is of 140 mw load capacity bay to be replaced by 400 mw capacity bay.other than CT(1200/1) what are the other equipment i have to replace. why we generally use 3.5 core cable or in other word 1/2 core for neutral and also confirm me that in balance conditiob(3 phase)current in neutral will zero
how to decide the rating of the ct for 1500 kva transformer
when the flux enters into saturation mode then what will be the secondary voltage of the normal t/f?....high or low ? explain ...how?
How to calculate impedance volt in Transformer?
what is the function of step up transformer?
how to calculate the earth fault current
What phase difference between p and s winding of transformer
why the impedence of the transformer is expressed in percentage?
We have 800KW motor operating at 6600Volt,50 Hz supply.During 1st startup it tripped on overcurrent trip.It's FLA is 88 Amps.The K factor of Thermal overloaaad was set on .94 initially.then we set at 0.97 and then it started fine.i dont understand why it tripped first?What are the protections which comes in picture during starting ?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)