how to calculate knee point voltage of current transformer?
Answers were Sorted based on User's Feedback
Answer / gusu
knee point Voltage = Burden x aLf
-------------
Class
E.g:10VA 5P20 CT.
To Get the Knee Point Voltage
=> 10VA x 20
--------- = 10 x 20
5P ------- = 40V
5
| Is This Answer Correct ? | 22 Yes | 49 No |
What is star-delta transformer?
High voltage test procedure of in swgr board. why should measure millivolt drop on testing time?
how would you determin the horsepower of a motor without a nameplate
How to identify the start and end of 3phase 12 lead motor if U1, U2, etc numberings are lost or erased.
what is the full name of ELCB &MDB <MCB
Explain the propagation of harmonics in the network and influence of phase angle of harmonics.
what is the proximity & ferranti effects can you explain to me
How to see the inductance in a transmission lines
I AM INTERESTED TO WIND A 3 PHASE MOTOR HOW I CALCULATE TURNS, PITCH,AND WIRE SIZE FROM STATOR DIMENTIONS
WHAT IS LIGHTNING,HOW TO CALCULATE LIGHTNING DESIGN CALCULATION?
formula for calculation of switchgears(i.e. contactor, fuse, cb, relay etc.), if load current is given?
how we calculate electricity unit ( meter unit.. for knowing how many charges) from on motor load.?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)