During the main stator winding insulation testing (phase to ground)of 11kv alternator (Lerysomer) i found 0 and resistance with multimeter and found 20 killo ohm while the power cables are connected both end (Generator & VCB). In VCB PT (Potential transformer) are connected.
Please any body explain that method of insulation is correct or not? also describe of PT connections
Supposing that you have disconnected the neutral of GEN , you will measure the dc resistance of PT as the other end of it is earthed . 20 K ohm will be measured as 0 M ohm by the megger . If you want to test insulation of GEN , you have to isolate the winding from everything .
Is This Answer Correct ? | 0 Yes | 0 No |
why we avoid parallel operation of diesl generator?
length of 4 core cable 95mm from substation LV VFD panel to Motor at field approximately 150 meter. Motor stop and power has been isolated from LV MCC ( Substation )to disconnect Motor for services. After Motor completed service propose to reinstall and reconnect Motor Cable, found earth cable sparkling during touching at metal / motor body. Inspect by clamp meter found earth cable have current flow AC 1-2amps and all earth cable at MCC LV also have current flow as same value. why it is happen?
what is anode and cathode??
if we run a 3 phase machine on two phase what will happend??? given answer with solid reason please
Difference between mcband isolator
Whats the type of current and potential transformers?
haw to calculate resistance of induction motar
How Can we calculate current carrieng capacity of Copper Bus-Bars and Alluminium Bus-bar
What is meant by full pitched winding?
What is Phase margin?
How do we calculate transformer oil in liter from the rating of the transformer.
what is bushing in transfermor
7 Answers Bokaro Steel, Visa Steel,