During the main stator winding insulation testing (phase to ground)of 11kv alternator (Lerysomer) i found 0 and resistance with multimeter and found 20 killo ohm while the power cables are connected both end (Generator & VCB). In VCB PT (Potential transformer) are connected.
Please any body explain that method of insulation is correct or not? also describe of PT connections
Supposing that you have disconnected the neutral of GEN , you will measure the dc resistance of PT as the other end of it is earthed . 20 K ohm will be measured as 0 M ohm by the megger . If you want to test insulation of GEN , you have to isolate the winding from everything .
| Is This Answer Correct ? | 0 Yes | 0 No |
How the main bus bar rating of 400kV switchyard with one and half breaker scheme is calculated.
why the rating of transformer in k.v.a
Why servomotor and induction motor are in different shape
what happen if the parallel generator phase angle shift by 1 degree in manual mode
why generaotr rating is in kva and dc motor in kw?
working function importance of mdc meter
What are the types of transformers according to the arrangement of iron cores?
Which element has power dissipated in it when the source is removed ?
diameter of cable and core is doubled then the value of capacitance is
what is power system transient condition
Relation between pyramids and electrical technology?
why one pin of plug pin is longer than other two? In some mobile chargers one pin is made not conducting .Why?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)