Answer / ashli
induction motors are of two types- squirrel cage and phase
wound motors. in squirrel cage motor as the rotor
conductors are shorted by endrings its not possible to add
additional resistance.but we can limit the current by
reducing the supply voltage at starting. here the high
current inrush is limited by star-delta starter.ie at the
instant of starting the stator winding is connected in star
der by voltage per phase becomes V/(3)^.5.. after the rotor
attains sufficient speed the stator windind is made delta.
in phase wound type motor the rotor condutors are shorted
through resistors. and current is limited by applying
resistors
synchronous motor is not a self starting one. syn motor is
made to rotate at syn speed firstly only then 3 p supply is
given to the armature. so no question of high current arises
| Is This Answer Correct ? | 26 Yes | 5 No |
Answer / lovkesh arora
Whenever you start a big heavy electric motor, you need to
start it slowly to prevent the rotor overheating and
drawing an enormous current. When the windings of a 3-phase
motor are connected in STAR the current is reduced to only
root three of the normal running current that is taken when
it is connected in DELTA.
Once the motor picks up speed, the connection is changed to
DELTA so that the motor runs at full speed and torque from
then on. It's a bit like using the gears of an automobile.
| Is This Answer Correct ? | 12 Yes | 1 No |
types of starters in ac motor
1. Rotor resitance starter-it is used only for Slip ring
in squirrel cage IM is wound rotor so we cant add external
resistance.in starting resistances are included to limit
the starting current.
2. star delta starter-at the time starting the rotor is
connected as star and in running itis connected as delta.
it can be used for both slip and Squirrel cabe IM.
3. Auto transformer starter- at the time starting by using
auto transforme the voltage is reduced.
4. DOL starter - it doesnt reduce any staring current. it
is used only for small rating of motor
| Is This Answer Correct ? | 12 Yes | 4 No |
Answer / l.veeraragavan
Normally starting current of induction motor is 6 to 7
times of the full load current.This because high
inersia(mass) of the rotor.So more current require to
move this rotor.So if we insert he resistance in series
with ckt (in starting only, after starting we gradually cut
this resistance from Ckt) ,we can reduce this starting
current. i.e The function of the starter is inclde
resistance during,after starting it will gradullay cut the
resistance.
| Is This Answer Correct ? | 8 Yes | 3 No |
Answer / venu
Mainly starters are used to reduse the starting
current.normally we will use the star delta starter for the
above 7.5HP.
as per the electrical formula.
motor will start in star first
since IL = IPh
coz we have to equilize the starting current
then its go to delta
Since VL= Vph
Finally
In star -Current equal
In Delta- Voltage equal
that how the starter will control the startingcurrent
| Is This Answer Correct ? | 4 Yes | 2 No |
Answer / jaggu
Induction motor is similar in action to a poly phase transformer with short cktd secondary which is rotating. if normal voltage is applied to the motor then the motor will draw a large current at the start. Induction motor when directly switched on takes 5-7 times their full load current. This can damage motor winding and generate large voltage drop, which may affect other equipment operation. Therefore IM while starting uses following starters:
1) Direct online starter
2)Stator resistance starter
3)Auto transformer starter
4)Star-Delta starter and
5)Rotor resistance starter- only in the case of slip ring IM
| Is This Answer Correct ? | 3 Yes | 1 No |
How can we connect additional batteries to three phase ups? What are parameters we have to check when connecting?
whose the first invented AC voltage or DCvoltage
What will happen if the 50HZ Transformer is connected with 60HZ power Supply
What is capacitance?
Why we apply only reduced voltage to the alternator while conducting slip test ? also the current increases to a larger value with reduced voltage itself Why ?
what do you mean by PF correction. A motor is rated at 15 kw,415 volts, 0.7 pf and eff of 0.92. The powerfactor is improved to 0.98 by adding capacitors at the bus. calculate the current drawn by motor under full load condition before and after pf correction
What is clock position of Transformer?what are the clock positions are there?and what is different of them?
What should be the magnetic balance test values for a 3 phase delta/star connected single primary dual secondary winding transformer (90 MVA / 2 X 45 MVA TRANSFORMER)
what is purpose of using reactor in substations
What will happen if DC supply is given on the primary of a transformer?
Give the selection criteria of a 3 Phase transformer for industrial purposes ?
why the auxilary(starting)winding is provided in single phase inductoin motor?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)