What will happen if the 50HZ Transformer is connected with
60HZ power Supply
Answers were Sorted based on User's Feedback
Answer / k.prakashchandra
Nothing, as the flux will be less for the same voltage.Iron
losses increase.
Is This Answer Correct ? | 14 Yes | 2 No |
Answer / hanumanth reddy
here two cases will arise.if supply voltage is constant the hysterises loss will decrease and eddy current loss constant.Then total loss will decrease.
if supply voltage is not constant means voltage also increases proportional to the frequency the eddy current losses and hysterises loss increases.
Is This Answer Correct ? | 0 Yes | 0 No |
how can service sitting be setted for MCCB?Example for sittings IR (CURRENT RATING),IS(CURRENT STARTING)IO (current operating)?
What is difference between SMC supportg and Glass Fibre Reinforced Plastic Support.
How to calculate Air conditioning capacity for a telecom BTS shelter?
Why does the power consumed is always constant even if a fan speed is altered?
lightning current is ac or dc..?????
What is the difference between DOL starter and star delta starter
In aircraft,why we use 400 htz equipment.and use common earthing
Transformer TTR test procedure
Explain few advantages of electric traction system?
what is formula in determining the size of Circuit Breaker for transformer with the following specifications. 7 units of 1600 volts (primary) and 400 volts (secondary). Both Primary and Secondary will have a circuit breaker which is SF6. What should be the Switchgear Main Breaker Size anf the sizes of each brances Circuit Breaker for Primary.
Dear Friends, I have a 500KVA transformer supplying whole factory having 3 phase and single phase mixed loads. Power room has ammeters connected via CTs for individual phase. Now I know that readings shown on meter for each phase say R,Y and B are line currents. But when I want to know the total on transformer do I need to add the currents of all three phases readings shown on meter or value for anyone phase will give me the correct power load on transformer for that point of time. 2. If ammeter shows unbalanced readings for R,Y, B phases say 150, 250 and 300 respectively so can I assume that 150A i.e average of 3 will be the 3phase load currents and remaining will be 1phase currents. Please clarify my doubt.
what is the necessity of under ground cables ??