Give the selection criteria of a 3 Phase transformer for
industrial purposes ?
Answers were Sorted based on User's Feedback
Answer / tauseef tarique, engineer(e)
For the selection for the transformer first calculate the
total load and then apply the diversity factor.
Is This Answer Correct ? | 11 Yes | 2 No |
Answer / deepankar
These points must be
taken into account...
~voltage required
~transformer
connection
~total connected load
~demand factor
~1.5 times safety factor
Is This Answer Correct ? | 5 Yes | 0 No |
Answer / gunasekaran
1.fault level
2.load current
3.voltage tip at starting the inductive load
4.type of load.
Is This Answer Correct ? | 5 Yes | 3 No |
what will be the energy loss =? Voltage drop = ? Conductor resistance at 20 degree C = ? Temprature convertion Factor at 50 degree c = ? on ACSR DOG Condutor at following data. distance = 4.8 kM Load = 2980 kWh Size of Conductor = 6/ 0.186 Volt = 11 kV.
1 Answers Pakistan Atomic Energy Commission PAEC,
If a surge divertor is required to be protected by 32 amp C Curve Circuit breaker does this limit the amount of protection from surges that you will acheive
what is the formula for calculate the turns in Transformers
ups and invertor battery selection chart and full formula
what is a pulse transformer? how rise time of pulse changes when ever the voltage changes?
during installation time of transformer and alternator which points we have to observed?
what is the function of rccb how it diffrentiate between elcb
140 is load amps for a equipments and what ratio of CT requied for installimg ammeter to amps montering purpose?
How to check op amp using multimeter