why C.T secondary are rated 5A generally?
Answers were Sorted based on User's Feedback
Answer / ashim kumar das
Its basically depends on the circuitry, whether you are
using it as a metering CT or a Protection CT.
For metering purpose generally 5A CT is used, because the
VA drop occurd in the cable between CT and the metering
instrument doesn't much harmfull for the system.
But for protection purpose 1A CT is recommended, because if
the distance between the CT and the protection relay is
very large, the VA drop occurd in the cable can give
reduced current reading to the instrument and this will be
a thread to the machine.
| Is This Answer Correct ? | 40 Yes | 2 No |
Answer / shekhar
it is because that secondary of c.t is connected to relay
to trigger it when any fault occurs.
primary of c.t carries fault current so very high value so
to protect the equipment the secondary is low.
it is in the range 0-10A
| Is This Answer Correct ? | 15 Yes | 13 No |
Answer / rahul
more of our meter & relay are of 1A to 5A range to operate
because the accuracy,loss & stability factor so alwayes the
CT O/P is 1A to 5A
| Is This Answer Correct ? | 1 Yes | 1 No |
Answer / rajiv
what is the maximum rating of ct can we measure below 1 amps
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / eng . ammar al-qudah
it depends on the purpose of the CT , when we install the CT before a protection device , a 5A CT will be installed for the most protection device , and when the CT are needed for measurement system the choice will be 1A for more accuracy , so we can't give a certain answer for this , it depends where we use it .
| Is This Answer Correct ? | 2 Yes | 3 No |
Answer / mahamuni raja
this is not a standard case the CT secondary shall be 5A.
moreover it depends upon the purpose,for protection
generallly will use 5A and for metering 1A. however while
selecting 5A the voltage drop will occur also didtance
between the metering and the protection relay.
| Is This Answer Correct ? | 7 Yes | 10 No |
Answer / puneet kumar
because current is measure by ammeter whose rating is up to
5 amp.(at secondry side of CT - CT is used only to reduce
the level of current at the measurable and safety level)
since we konw that CT has only 1 turn at primary
side becuase current is at higher value, to reducing it we
provide more turns at secondry side.. and this value can
measure by 5 amp. ammeter easily.
In power system, CT is used as protection device
also, which give signal to relay for operate under when
current become more than 5 amp.(at secondry side)
Therefore, CT secondry are rated 5A generally.
| Is This Answer Correct ? | 0 Yes | 3 No |
Answer / anthony
relays are connected to the sec. of a ct . If a large
rating is proposed for the sec. of the ct then it would
mean that the magnetising current (emag. relays) would be
high too, since on the sec. side you have an inductive
relay. This would actually present itself as a load on the
sec.of the ct .
| Is This Answer Correct ? | 2 Yes | 6 No |
Answer / karthik
#it is depent up on the round value for our calculation.
# the relay specification
# standrd form
| Is This Answer Correct ? | 2 Yes | 8 No |
Answer / arun
The CT has separate primary and secondary windings. The
primary winding which consists of few turns of heavy wire,
wound on a laminated iron core is connected in series with
one of the line wires. The secondary winding consists of a
greater number of turns of a smaller size of wire. The
primary and secondary windings are wound on the same core.
The current rating of the primary winding of a CT is 100 A.
The primary winding has three turns and the secondary
winding has 60 turns. The secondary winding has the
standard current rating of 5A;therefore the ratio between
the primary and secondary current is 100/5 or 20/1.The
primary current is 20 times greater than the secondary
current. Since the secondary windings 60 turns and the
primary winding has 3 turns, the secondary winding has 20
times as many turns as the primary winding. For a CT the
ratio of primary to secondary currents is inversely
proportional to the ratio of primary to secondary
turns..this 5A s the standard fixed by the electricity
corporation and they folow t..so its a convention to follow
this standarrdd
| Is This Answer Correct ? | 11 Yes | 19 No |
CAN 50Hz transformer work at 60 Hz power supply? if yes how it is possible?
i have to install a HT panel, what components, I have to use in this and what will the diagram of that diagram,please tell me each and everything.
i am trying to PSUs/govermeant jobs since last 2 years but still i m not success, plz help me.
can anyone provide me a amf panel control wiring using ec-2 relay?
how net resistance islow in star connection and viseversa in delta connection...? if anybody could explain in detail it wud be helpful.
pls someone send me sample question papers along with the key.thanks in advance
can SMPS work in DC supply ?
10 Answers HCL, IBM, Reliance,
Whether IP65 enclosure box blocks ventilation if driver for LED have to enclosed inside IP65 box
How to calculate size of HT breaker with the help of Amp (current)? Please provide answers with examples.
What is dc current source?
why we use ac supply as 415 volts instead of 415 v why we cant apply 230 v for dc
what is the back ground of transformer working? applying voltage to primary and emf inducing in primary and secondary? how it is possible? please answer me with scientific approach?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)