Whats meant by trivector meter where it is connected at the
substation?
Answers were Sorted based on User's Feedback
Answer / guest
trivector meter can measure active power ,reactive
power ,apparent power i.e.with the help of a single meter
we can measure kva,kw,kvar.
Is This Answer Correct ? | 307 Yes | 27 No |
Trivector meter is Electronic type Energy Meter which
measures energy parameters, like active energy, Reactive
energy,apparent energy, Power Factor, frequency etc.
Through which we can know how much enregy recieved or
sent.Trivector meter has 2 types, one is 3ph 3wire meter n
other is 3 ph 4wire meter.
It is conneceted in the substation to incoming or outgoing
feeders to know how energy is given out or recieved from
other end, or to Transformers on HV n LV side to know the
Transformer loss.
Is This Answer Correct ? | 252 Yes | 27 No |
Answer / venkat iyer
Tri-energies are Apparent, Active and Reactive. These are
expressed in three vectors. A single meter that measures
these three energy details are called a Tri-vector meter.
This is clear from the name of the instrument itself.
Is This Answer Correct ? | 94 Yes | 11 No |
Answer / mohit bharti
trivector means 3 types of power i.e.
1.VA= V*I
2.Watt = V*I*cos Wt
3.VAR = V*I*sin wt
where:-
v= applied voltage.
i= resultant current.
wt=phase ange between them.
a singe divice can measure all 3 power at a time.
normally at substations this term is used for feeder
input/outgoing power.trivector meter is also of 2 types:
HT meter connected at high Tension side of transformer.
LT meter connected at Low Tension side of a trnsformer.
Because in high tension line voltage is of 11 KV and above
range and this type of meters have not made which connected
directly in high tension line so it's connected with PT
(potentail transformer)which step down the voltage and
meter recieved this voltage.In meter software PT ratio is
already known by the manufacturer.
For exampe if a high tension line voltage is 11 kv line to
line and PT ratio is 100 then meter actually reads
11000/100= 110 volt line to line and in software
calculation it reads the actual reading by PT ratio.
So VA power is calculated by meter is
VA= 110*current*PT ratio
some time a CT(current transformer) is also used for
current measuring and CT ratio is known.then calculation is
VA= voltage*PTR*current*CTR.
Normally PT is used for HT Line and CT is used for LT line.
Is This Answer Correct ? | 62 Yes | 7 No |
Answer / pradyumna kumar jena
There are 3 types of electrical ernergies. These energy
parameters are vectors. They follow the Phythagourous
theorem. 1. VI, 2. VICos(phi), 3. VISin(phi). The sequence
is Apparent, Active and Reactive. Any meter, which
measuring all these three vectors is called Trivector. It
may be single or Three Phase, not an issue.
Is This Answer Correct ? | 27 Yes | 14 No |
Answer / chandrakant sahu
Most of the Tri-Vector Meter Are basically Measure Following
Bi-Directional Parameters :
1. Phase Wise Voltage
2. Phase Wise Current with Neutral
3. Phase Wise Power Factor with Total
4. Phase Wise kW with Total
5. Phase Wise kVA with Total
6. Phase Wise kVAR with Total
7. Frequency (Avg. Frequency)
8. ToD Demand / Energy
9. Import kWH / kVAH / kVARH - Lag / kVARH - Lead
10. Export kWH / kVAH / kVARH - Lag / kVARH - Lead
11. THD
This Meters can be used LT / HT / ABT based on the Capacity
of Feeder on which this Meters are to be installed. CT / PT
Ratio can be configured for such Meters.
Is This Answer Correct ? | 23 Yes | 10 No |
Answer / ashraf
As the name suggests it is an electronic meter which is
used to measure the KWH,KVAH & KVARH.
it was originaly designed to measure the apparent power,
reactive power & active power. But now a days modern
trivector meter can also measure the power factor,
frequency & other electrical parameters in addition to
these three.
may be instaaled at HV or LV side, input/output side of
power transformer so that the consumption of energy can be
measured.
Is This Answer Correct ? | 15 Yes | 6 No |
Answer / chakra babu gundra
*.The Trivector meter is a measuring instrument which measures the Active Power, Reactive Power and Total Energy consumed of a power line.*.Trivector meters are normally used in substations and to measure the power flowing through the feeders.*.They are also usedfor billing power drawn by industrial customers.
Is This Answer Correct ? | 3 Yes | 0 No |
Answer / shanker malagamma
yes, indeed trivector means the which measures energy in
three vector i.e active energy(kwh), reactive energy(kvarh)
and apparent energy(kvah) using single meter and it is
connected to incoming and outgoing feeders in the
substaion. Trivector meter may in four quadrant or may not
be four quadrant, if it is four quadrants then it is called
as Trivector meter with import-export facility or if it is
in any two qudrants i.e either import only two qudrants or
export only quadrants then it is called as TVM with import
only facility or TVM with export only facility. normally
former one will be manufactured than later.
Is This Answer Correct ? | 25 Yes | 23 No |
Answer / sundar
I too here not giving answer, but i want know more about that two quadrant and four quadrant form Mr.Shankar Malagamma.Sir can you explain that in detail.
Is This Answer Correct ? | 2 Yes | 1 No |
WHAT IS A DIFFERENCE BETWEEN A DC GEAR MOTOR AND STEPPER MOTOR.AND WHICH IS MORE APPROPRIATE TO USE FOR POSITION CONTROL PURPOSE?
After fault clearing in Tr line, whether the Metering core of CT is comes to normal condition from saturation region & its works as a normal condition?
How can calculat the lode of transformer?
In a synchronous motor armature current flows due to revolving flux which in turn rotates the load,but in no load condition armature current is zero hence thr is no revolving flux then how motor rotates?
what is a difference b/w earthing & neutral?
what is the CT & PT. where is it uses.what is the using that plese kindly answer me...?
a.c&d.c motor&generator
what are the protection equipments used betbeen HT line and transformer in a power plant
why leading pf indicates a negative sign???
what size steel armoured cable is required to support 1500kva capacity. would 70mm squared be enough or would I need 90 or 120mm squared 3c plus earth
how nautral is provided for return path is 3 phase induction motor
what is the difference between power transformer & distribution transformer and what are their ratings respectively?