Answer / amit
For transformer these are the fallowing test should be taken
1) Insulation resistance test
2) Vector group test
3) Transformer oil Break down voltage test
4) Magnetic current & Ratio test
5) Magnetic balance test
6) High Voltage test
7) Transformer winding rasistance test
8) PI Value test
9) SC test
10)OC test
| Is This Answer Correct ? | 82 Yes | 10 No |
Answer / zahid ali
On transformer
1- Insulation Resistance
2- Di-electric loss Factor or Tan delta or Power Factor test
3- Polarity & Vector Group Test
4- Transformer Turn Ratio Test
5- Sweep Frequency Response Analysis
6- Temperature Rise Test
7- AC leakage Test
8- Dissolve Gas Analysis Test On Oil
9- Short Circuit & Open Circuit Test To determine losses
On Generator
1- Insulation Resistance & Polarization Index
2- Hi Pot
3- Short Circuit Test
4- Power Factor Tip up test
5- Partial Discharges Test
6- El Cid Test (electromagnetic core imperfection detection)
7- Retaining Ring Test (Ultrasonic)
8- Recurrent Surge Oscillation Test on Rotor (RSO)
9- Low Resistance Test
10- AC Leakage Test
| Is This Answer Correct ? | 48 Yes | 7 No |
Answer / sachin rai
HI I am sachin rai working in mahindra automotive
sector,pune, here is the list of all tests carried out of
testing transformer. if u want know more about it pls mail
at rai.sachin21 @gmail.com
1. Voltage ratio test To measure voltage ratio between
windings of transformer
2. Polarity
3. Phase relation test
4. Resistance measurements
5. No-load loss test
6. Exciting current test
7.Load loss and impedance test
8.Induce potential test
9. Applied potential test
10. Oil test
11. Insulation resistance test
12. Leakage test
13. Temperature-rise test
14. Dielectric type test (Lightning and switching Impulse
test, BIL)
15. Dielectric special test BIL FW&CW
16. Determination of capacitance winding-to-earth, and
between windings
17. Measurement Zero-sequence impedance on three phase
transformer
18. Determination of sound level
19. Measurement of the dissipation factor (tan d) of the
insulation system capacitance
20. Determination of partial discharge on transformer
| Is This Answer Correct ? | 22 Yes | 1 No |
Answer / ketan y more
I AM KETAN MORE
1) MEGGER TEST
2) INSULATION TEST
3) POLARITY TEST
4) INSULATION RESISTANCE TEST
5) RATIO TEST
6) OPEN CIRCUIT TEST
7) SHORT CIRCUIT TEST
8) HV TEST
9) INDUCED TEST(TVTF_)
10) MAGNETIC BALANCE TEST
11) VECTOR GROUP TEST (DYN11)
| Is This Answer Correct ? | 12 Yes | 2 No |
Answer / vishwas shinde
no load test,open circuit test,voltage ratio testmeasure of
winding resistance test.
| Is This Answer Correct ? | 8 Yes | 4 No |
Answer / vipul parmar
1.Insulation Resistance Test
2.Winding Resistance Test
3.Magnetizing Current Test
4.Magnetic Balance Test
5.Voltage Ratio Test
6.Open Circuit Test
7.Short Circuit Test
8.High Voltage Test
9.Double Voltage Double Frequency Test
10.PI Test
11.SFRA Test
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / shilpesh naik
whether the short circuit test is to be caried out on every
transformer.......as it is a destructive test....which can
affect the windings of the transformer..........
| Is This Answer Correct ? | 0 Yes | 2 No |
Answer / nageshwaran.n
a. Insulation Resistance Test
b. No Load Test
c. Full Load Test
d. Oil Check
e. pf Test
f. Leakage Test
g. Open & Close Circuit Test
h. Sweep Frequency Test
| Is This Answer Correct ? | 7 Yes | 10 No |
circuit diagram of trip circuit supervision relay
My switchgear busbar is rated at 2000A and just imagine the actual load on busbar is 1000A. From that busbar there are 10 outgoing feeders. Now the question is will the load be 1000A on each outgoing feeder or 100A per outgoing feeder. 2nd thing how do i calculate the load on individual feeder. Thanks for your time. Please provide some clarification on this issue.
what are the major & minor faults that occur in an inverter and in UPS ? And how to repair and resolve them ?
How many types of probe used in cro?
how kva rating of transformer is calculated.
6 Answers Fluor Daniel, Siemens,
why power generate in 33 kv it will be step down by 11 kv .
please suggest some good universities with low cost iam in totally full confusion so please help me my profile gre 283 and ielts 5.5
what happen if the secondry winding of the transformer is having less no of turns compare to the primery winding.
What is a Servo Stabliser.
what is MFD value in capacitor?I have 201 Kva load & reactive power is 150 Kvar. so how it is calculated?
what is the d/f b/w iverter & converter.
What is the method of Tan delta test for power Transformes and why it is required.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)