Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


What are the tests to be taken on a transformer and
generator?

Answers were Sorted based on User's Feedback



What are the tests to be taken on a transformer and generator?..

Answer / amit

For transformer these are the fallowing test should be taken

1) Insulation resistance test
2) Vector group test
3) Transformer oil Break down voltage test
4) Magnetic current & Ratio test
5) Magnetic balance test
6) High Voltage test
7) Transformer winding rasistance test
8) PI Value test
9) SC test
10)OC test

Is This Answer Correct ?    82 Yes 10 No

What are the tests to be taken on a transformer and generator?..

Answer / giridhar

sc test & oc test done on t/f, no load,load test

Is This Answer Correct ?    60 Yes 9 No

What are the tests to be taken on a transformer and generator?..

Answer / zahid ali

On transformer
1- Insulation Resistance
2- Di-electric loss Factor or Tan delta or Power Factor test
3- Polarity & Vector Group Test
4- Transformer Turn Ratio Test
5- Sweep Frequency Response Analysis
6- Temperature Rise Test
7- AC leakage Test
8- Dissolve Gas Analysis Test On Oil
9- Short Circuit & Open Circuit Test To determine losses
On Generator
1- Insulation Resistance & Polarization Index
2- Hi Pot
3- Short Circuit Test
4- Power Factor Tip up test
5- Partial Discharges Test
6- El Cid Test (electromagnetic core imperfection detection)
7- Retaining Ring Test (Ultrasonic)
8- Recurrent Surge Oscillation Test on Rotor (RSO)
9- Low Resistance Test
10- AC Leakage Test

Is This Answer Correct ?    48 Yes 7 No

What are the tests to be taken on a transformer and generator?..

Answer / sachin rai

HI I am sachin rai working in mahindra automotive
sector,pune, here is the list of all tests carried out of
testing transformer. if u want know more about it pls mail
at rai.sachin21 @gmail.com
1. Voltage ratio test To measure voltage ratio between
windings of transformer
2. Polarity
3. Phase relation test
4. Resistance measurements
5. No-load loss test
6. Exciting current test
7.Load loss and impedance test
8.Induce potential test
9. Applied potential test
10. Oil test
11. Insulation resistance test
12. Leakage test
13. Temperature-rise test
14. Dielectric type test (Lightning and switching Impulse
test, BIL)
15. Dielectric special test BIL FW&CW
16. Determination of capacitance winding-to-earth, and
between windings
17. Measurement Zero-sequence impedance on three phase
transformer
18. Determination of sound level
19. Measurement of the dissipation factor (tan d) of the
insulation system capacitance
20. Determination of partial discharge on transformer

Is This Answer Correct ?    22 Yes 1 No

What are the tests to be taken on a transformer and generator?..

Answer / ketan y more

I AM KETAN MORE


1) MEGGER TEST
2) INSULATION TEST
3) POLARITY TEST
4) INSULATION RESISTANCE TEST
5) RATIO TEST
6) OPEN CIRCUIT TEST
7) SHORT CIRCUIT TEST
8) HV TEST
9) INDUCED TEST(TVTF_)
10) MAGNETIC BALANCE TEST
11) VECTOR GROUP TEST (DYN11)

Is This Answer Correct ?    12 Yes 2 No

What are the tests to be taken on a transformer and generator?..

Answer / vishwas shinde

no load test,open circuit test,voltage ratio testmeasure of
winding resistance test.

Is This Answer Correct ?    8 Yes 4 No

What are the tests to be taken on a transformer and generator?..

Answer / vipul parmar

1.Insulation Resistance Test
2.Winding Resistance Test
3.Magnetizing Current Test
4.Magnetic Balance Test
5.Voltage Ratio Test
6.Open Circuit Test
7.Short Circuit Test
8.High Voltage Test
9.Double Voltage Double Frequency Test
10.PI Test
11.SFRA Test

Is This Answer Correct ?    2 Yes 0 No

What are the tests to be taken on a transformer and generator?..

Answer / shilpesh naik

whether the short circuit test is to be caried out on every
transformer.......as it is a destructive test....which can
affect the windings of the transformer..........

Is This Answer Correct ?    0 Yes 2 No

What are the tests to be taken on a transformer and generator?..

Answer / nageshwaran.n

a. Insulation Resistance Test
b. No Load Test
c. Full Load Test
d. Oil Check
e. pf Test
f. Leakage Test
g. Open & Close Circuit Test
h. Sweep Frequency Test

Is This Answer Correct ?    7 Yes 10 No

What are the tests to be taken on a transformer and generator?..

Answer / ramarpandi

megger test

Is This Answer Correct ?    4 Yes 11 No

Post New Answer

More Electrical Engineering Interview Questions

circuit diagram of trip circuit supervision relay

0 Answers  


My switchgear busbar is rated at 2000A and just imagine the actual load on busbar is 1000A. From that busbar there are 10 outgoing feeders. Now the question is will the load be 1000A on each outgoing feeder or 100A per outgoing feeder. 2nd thing how do i calculate the load on individual feeder. Thanks for your time. Please provide some clarification on this issue.

1 Answers   Alstom,


what are the major & minor faults that occur in an inverter and in UPS ? And how to repair and resolve them ?

0 Answers  


How many types of probe used in cro?

0 Answers  


how kva rating of transformer is calculated.

6 Answers   Fluor Daniel, Siemens,


why power generate in 33 kv it will be step down by 11 kv .

5 Answers  


please suggest some good universities with low cost iam in totally full confusion so please help me my profile gre 283 and ielts 5.5

0 Answers  


what happen if the secondry winding of the transformer is having less no of turns compare to the primery winding.

2 Answers  


What is a Servo Stabliser.

2 Answers  


what is MFD value in capacitor?I have 201 Kva load & reactive power is 150 Kvar. so how it is calculated?

2 Answers   IIT,


what is the d/f b/w iverter & converter.

5 Answers   Indeco,


What is the method of Tan delta test for power Transformes and why it is required.

1 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)