What are the tests to be taken on a transformer and
generator?
Answer Posted / amit
For transformer these are the fallowing test should be taken
1) Insulation resistance test
2) Vector group test
3) Transformer oil Break down voltage test
4) Magnetic current & Ratio test
5) Magnetic balance test
6) High Voltage test
7) Transformer winding rasistance test
8) PI Value test
9) SC test
10)OC test
Is This Answer Correct ? | 82 Yes | 10 No |
Post New Answer View All Answers
what's the difference between abs/inc encoders. apart from the position remembrance what are all the other differences. and what's mean by grey code.
what curve and rateing would you use for a three phase 0.75kw motor?
what is mean by PIR in circuitbreaker and give me detail of that?
what is the need of starter in tube light and what type of starter is used in that?
What is Phase margin?
What is the tipical Online UPS input voltage for 20 KVA load ( 3 Phase or 1 Phase )? Why ? Explain it...?
how ceiling fan worked?
What are the types of transformers according to the arrangement of iron cores?
Merits & Demarits of Oil circuit & Air circuit breakers ?
What is the phase relationship between the primary and secondary voltages of a transformer?
testing of Vector Group – YNaoD II
pls,send the previous year written test questions.
Explain the experiment on ward leonard method of a speed control on a dc shunt motor with an suitable circuit diagram.
A well system is when , no. of bus bar is less or more. Tell me the concept of it.
i need the curve duty cycle and amper for (150 kva @50% dyty cycle) transformer turn ratio :19 and vin 400