Make a list of materials and layout diagram for a 35hp motor, to be wired at 35meter away from the MDB in a chemical factory.
Answers were Sorted based on User's Feedback
Answer / a.yogeswaran
1 hp =750watts
35hpx750=26250
total load P=26.25
current I=26.25X1.74
=45.675(not in market)
=63A
cable size will be as 25cumm2 XLPE/SWA/PVC and 16cumm2 Y/G.CU.PVC.ECC(as required)
Breaker=63A 100mA ELCB Breaker
MDB 01 QUANTITY
Bus Bar Size=20mmx10mm
| Is This Answer Correct ? | 8 Yes | 2 No |
Answer / waleed hourieh
P=35*746= 26.11 kw
I= 26.11 *1.74*1.25=56.7a
So the CB = 63A.
Materials list :
63A TP MCCB .25KA
63A/100mA ELCB .
60*60 MANHOLE COVER HEAVY-DUTY
35METER UPVC BLACK PIPE HEAVY-DUTY
4C*25MM2+1C*16MM2 Y/G.= 38 METER
63A TPN ISOLATOR
| Is This Answer Correct ? | 0 Yes | 1 No |
What is burden of ct,explain very simple
which will glow brighter?bulb 1 (110v,100w) and bulb 2 (230v.200w) series connection
we have 2.2kw,Y,3000rpm motor but 6leads found in TB what happen if we connect in delta?
can any one provide me a connection wiring diagram for a DG set control panel along with BOM?
Why in india freq. is 50HZ & in U.S.A. it is 60HZ?
why colour of electrical equipment( like transformer) is grey
what is function of reactor coil in Power factor correction panel
practicalLY what is impedence ...?
What is meant by harmonic distortion?
Why heat produce in AC machine higher than DC machine?
I want d.g.set our company
If increased the frequency up to 1000 then what changes shows in voltage?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)