We have yokogawa cs3000 one fcs and 4 his. After download to his, showing successfully at es, but not transferred to his.
Dear,
First of all question is not clear that you are downloading what ? presume that you are downloading Graphics as other configuration will be downloaded to FCS and then automatically it will be "Equalized" to all HIS.
When you download any graphic in Engineering work station, the particular graphic will not appear in HIS unless you have pasted same graphics shortcut to any HIS. So, you can follow this procedure :
1) PASTE shortcut in respective HIS.
2) Once you download the required graphic in Engineering workstation the close the builder and select the particular graphic and in TOOLS MENU select the option DOWNLOAD TO HIS.
By this your graphic will be EQUALIZED in all HIS where you have pasted the shortcut of that graphic.
Fell free to post your result or any further question on :
Jigar Anadkat
E-mail : anadkat.jigar@gmail.com
Is This Answer Correct ? | 3 Yes | 0 No |
WHY TEMPERATURE TRANSMITTER USED AS WE CAN CONTROL THROUGH THERMOCOUPLE/RTD
Is there a particular problem if two proposals from the same observatory (originating with different partners) are submitted?
What are the type of bonnets in the control valves?
What is transmitter
what is modbus,profibus,fieldbus
What is megering????
what is the protection system in solar turbine compressor
what is use single seated and double seated valve?
2 Answers Doha Petroleum Construction DOPET,
How a pH sensor & analyzer work at waste water treatment plant, whats the principle & science is beyond this,How pH sensor sence & convert signal & move toward analyzer & analyzer show reading in percent? also what is temperature compensate option in analyzer
what is the difference between impact plate n coriolis type solid flow meters n how they works....n which one is better
how to use K thermocouple instead E- type without compesation cable
please send me the inteview questions in IOCL