Actually why the transformers ate rated in KVA.?
Answers were Sorted based on User's Feedback
Transformer gives apparent power,it is the supply power to load and the power actually used by the load is the real power/true power/active power. Apparent power of 100 KVA has capacity to give 100 KW resistive load and for inductive load of o.8 pf it give 80 KW,and at 0.7 pf the same has capacity to give 70 KW . but the manufacturing company does not know which type of load to be connected across the transformer,therefore in simple we can say " DUE TO UNKNOWN POWER FACTOR THE TRANSFORMER ARE RATED IN KVA" and it is meaning less discuss about Iron loss & copper loss because the Inverted and UPS are rated in KVA but there is no iron loss & copper loss And in other hand in DC Generator there is Iron loss &copper loss but it is rated in KW not in KVA, because there is no angle between current and voltage(pf) in DC supply N.B transformer capacity -transformer iron loss & copper loss = transformer efficiency in KVA
PRADYUMNA CHANDRS PANDA
Mob No. 9437917849
| Is This Answer Correct ? | 22 Yes | 1 No |
Answer / santosh bangar
rating of any electrical equipment its depends on how much heating ( by losses) is permissible.
in Transformer , rated output limited by heating and hence by the losses in the transformer
two types of losses in transformer Copper loss( proportional to I) and core loss proportional to V)
we have constant power VI in transformer
if we increase Voltage then current will reduce
and if we increase current then voltage will reduce
we can not go beyond certain limit of voltage ... limited by core loss
and also can not go beyond certain limit of Current..limited by copper loss
means we know what is max voltage and max current and VI is rating of transformer
| Is This Answer Correct ? | 0 Yes | 0 No |
How one may guess the direction from which the distribution line is incoming if there is no pole plate on poles?
How one can say about a device (e.g: a light holder contains 20 or 30 L.E.Ds which glows when power supply is off, from which source they are getting the supply..... battery or capacitor) without removing and opening up its case ?
can anyone plz tell me in 3 phase induction motor, whare we use STAR CONNECTED MOTOR and whare we use DELTA CONNECTED MOTOR
Why primary batteries not rechargeable and secondary batteries are rechargeble??? If any one know please send me.
What are the causes of motor vibration?
My switchgear busbar is rated at 2000A and just imagine the actual load on busbar is 1000A. From that busbar there are 10 outgoing feeders. Now the question is will the load be 1000A on each outgoing feeder or 100A per outgoing feeder. 2nd thing how do i calculate the load on individual feeder. Thanks for your time. Please provide some clarification on this issue.
A ray hit a smooth regular surface at an angle of 20 from the normal. Calculate : 1. The angle btw the incident and reflection ray. 2. The angle of deviation.
What will happen if an AC induction motor is applied with DC voltage?????????Kindly give all the posssible answers...
What is working Priniciple of TVSS ????
Why we are using Ohm's law? where it is applicable? explain.
10 Answers Pyramid Saimira, TCS,
Can we calculate the P.F if we know the only load on alternator .
Why electrical engineer use Cu Strip for transformer neutral why not GI Strip? What if we use GI instead of Cu does it affects the transformer performance.
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)