Transformer gives apparent power,it is the supply power to load and the power actually used by the load is the real power/true power/active power. Apparent power of 100 KVA has capacity to give 100 KW resistive load and for inductive load of o.8 pf it give 80 KW,and at 0.7 pf the same has capacity to give 70 KW . but the manufacturing company does not know which type of load to be connected across the transformer,therefore in simple we can say " DUE TO UNKNOWN POWER FACTOR THE TRANSFORMER ARE RATED IN KVA" and it is meaning less discuss about Iron loss & copper loss because the Inverted and UPS are rated in KVA but there is no iron loss & copper loss And in other hand in DC Generator there is Iron loss &copper loss but it is rated in KW not in KVA, because there is no angle between current and voltage(pf) in DC supply N.B transformer capacity -transformer iron loss & copper loss = transformer efficiency in KVA
PRADYUMNA CHANDRS PANDA
Mob No. 9437917849
| Is This Answer Correct ? | 22 Yes | 1 No |
Answer / santosh bangar
rating of any electrical equipment its depends on how much heating ( by losses) is permissible.
in Transformer , rated output limited by heating and hence by the losses in the transformer
two types of losses in transformer Copper loss( proportional to I) and core loss proportional to V)
we have constant power VI in transformer
if we increase Voltage then current will reduce
and if we increase current then voltage will reduce
we can not go beyond certain limit of voltage ... limited by core loss
and also can not go beyond certain limit of Current..limited by copper loss
means we know what is max voltage and max current and VI is rating of transformer
| Is This Answer Correct ? | 0 Yes | 0 No |
How check proper electrical earthing of machine.
explain the working principal of the circuit breaker?
what is the principle of operation of synchronous motor and generator? explain in detail.
what's the different between ELCB, ELR and ELS?
what is power factor? how can we correction the power factor if this is high or low? If anyone know please please send the answer on my email id ( kumarkirshan@in.com )
I am working in 600MW power plant currently in erection phase. I came along this term and want to know its meaning in simple language, consider me naive!?? All motors shall be of energy efficient type EFF-2 as per IS:12615/ equivalent IEC / International Standard.
how much GROUND & NEUTRAL VOLT maintain in data center.
WHY FEEDERS TRIP IN COLD AND FOGY WEATHER?
area control error
Explain the operation carried out in thermal power stations?
when will be the iocl interview results i faced interview on 8th september 2008 iam from electrical branch i faced interview for the post of electrical engineer??????????????????????//
What happened ,If 3 phase clearance not maintained in 33KV Line,11KV LIne etc?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)