Transformer gives apparent power,it is the supply power to load and the power actually used by the load is the real power/true power/active power. Apparent power of 100 KVA has capacity to give 100 KW resistive load and for inductive load of o.8 pf it give 80 KW,and at 0.7 pf the same has capacity to give 70 KW . but the manufacturing company does not know which type of load to be connected across the transformer,therefore in simple we can say " DUE TO UNKNOWN POWER FACTOR THE TRANSFORMER ARE RATED IN KVA" and it is meaning less discuss about Iron loss & copper loss because the Inverted and UPS are rated in KVA but there is no iron loss & copper loss And in other hand in DC Generator there is Iron loss &copper loss but it is rated in KW not in KVA, because there is no angle between current and voltage(pf) in DC supply N.B transformer capacity -transformer iron loss & copper loss = transformer efficiency in KVA
PRADYUMNA CHANDRS PANDA
Mob No. 9437917849
| Is This Answer Correct ? | 22 Yes | 1 No |
Answer / santosh bangar
rating of any electrical equipment its depends on how much heating ( by losses) is permissible.
in Transformer , rated output limited by heating and hence by the losses in the transformer
two types of losses in transformer Copper loss( proportional to I) and core loss proportional to V)
we have constant power VI in transformer
if we increase Voltage then current will reduce
and if we increase current then voltage will reduce
we can not go beyond certain limit of voltage ... limited by core loss
and also can not go beyond certain limit of Current..limited by copper loss
means we know what is max voltage and max current and VI is rating of transformer
| Is This Answer Correct ? | 0 Yes | 0 No |
How can we estimate Gen rotor current?
Your B.tech marks is being given in CGPA grade. How is it calculated?
Is it possible to increasing the real power generation by reducing the reactive power in power generation plants
State uses of different types of stsrters with different capacities of motors as below: a. up to 5HP b. above 5hp to 10hp c. above 10hp to 20hp d. above 20hp
i want to do a project on PLC.... please give me an idea.....
what is use of reactive power in ac ckt.
how to convert single phase supply to 3 phase or 3 phase to single..?
CALCULATE THE TOTAL VOLTAGE DROP AND SELECT THE CABLE SIZE IN MM-SQARE FOR A PANEL-262KW AT 110 METER FROM THE SOURCE SUPPLY , SUPPLY VOLTAGE 240/415
What is the function of NGR for the parallel operation of alternator? whats happen when different rating of alternator are running with parallel?
why we are calculating the capacitance between phase(conductor line)and ground in transmission line?why cant we calculate capacitance between the phase and the nuetral line?if so what is procedure.
Waht is Inductor?
what is the best method of grounding in 30 MW generator?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)