Wat is the best to use in a generator a 6.5kva or a 7 kw
Answers were Sorted based on User's Feedback
Hi Jaswinder, the DGs are designed based on the load dependency only. If you are bring the DG in higher rating for low load then no meaning of efficiency.
Hence, 6.5 KVA or 7 KW(8.75 KVA) are doesn't matter. It is fully depends on the magnitude of load.
ersaravananp@gmail.com
Is This Answer Correct ? | 5 Yes | 0 No |
Generator ratings are always noted in KVA, not in KW. The ratings are designed based on the load dependency.
From your question,6.5 KVA is better than 7 KW(8.75KVA Aprox.)
ersaravananp@gmail.com
Is This Answer Correct ? | 3 Yes | 1 No |
Answer / jaswinder singh
I agreed that Generator rating is always noted in KVA. From
the question, 6.5 KVA Generator can run for 5.20 KW only
which less than 7 KW. So 7KW (8.75 KVA) DG set is better.
Is This Answer Correct ? | 1 Yes | 1 No |
Answer / simon
hiiiiiiiiiiiiiiii
6.5Kva=6500VA(250V*26Amp)IN 1Phase(440V*14.77Amp)in 3Phase
7Kw=7000W(250V*28Amp) in 1Phase (440V*15.9Amp)in 3Phase
Is This Answer Correct ? | 0 Yes | 0 No |
How to calculate no of EARTH PIT? Describe the formula as per IS standard?
what is protections used for 6.6kv ht motor
directional over current relay when acted & how it works
Why use in ht motore
A system having the charactristic eqation (s+1)(s+2)(s-3)=0 is (a)stable (b)unstable (c)marginally stable (d)critically stale
for leading power factor penalty by SEB why
why inuctive drop is not consider in DC MOTOR
Hello friends, Can anyone explain the concept of zones in Bus bar protection and how can we differentiate the main zone and check zone in Bus bar protection
what is the function of potential transformer in s/s
the electric traction poles having 3 cables n two cables touches with a insulator (or any) another one separated but it will be running 1-phase why?
How to calculate cable size in HT AND LT
in case of induction motor when overload condition or any short ckt. why stator winding burn not to be rotor winding