Hi Jaswinder, the DGs are designed based on the load dependency only. If you are bring the DG in higher rating for low load then no meaning of efficiency.
Hence, 6.5 KVA or 7 KW(8.75 KVA) are doesn't matter. It is fully depends on the magnitude of load.
ersaravananp@gmail.com
| Is This Answer Correct ? | 5 Yes | 0 No |
Generator ratings are always noted in KVA, not in KW. The ratings are designed based on the load dependency.
From your question,6.5 KVA is better than 7 KW(8.75KVA Aprox.)
ersaravananp@gmail.com
| Is This Answer Correct ? | 3 Yes | 1 No |
Answer / jaswinder singh
I agreed that Generator rating is always noted in KVA. From
the question, 6.5 KVA Generator can run for 5.20 KW only
which less than 7 KW. So 7KW (8.75 KVA) DG set is better.
| Is This Answer Correct ? | 1 Yes | 1 No |
Answer / simon
hiiiiiiiiiiiiiiii
6.5Kva=6500VA(250V*26Amp)IN 1Phase(440V*14.77Amp)in 3Phase
7Kw=7000W(250V*28Amp) in 1Phase (440V*15.9Amp)in 3Phase
| Is This Answer Correct ? | 0 Yes | 0 No |
During Starter Panel Com missing I Found The Main Incomer 40Amp MCB 10KA Trip When Motor Change Star To Delta Motor Rating 20HP BUT When We Use Same MCB To Other Motor It Does Not trip Or What Is Necessaries for Star Delta Starter MCB SFU MPCB OR MCCB And What are The Breaking Capacity of MCCB in the Motor above 15HP
Define noise?
what is the power factor of an inductive load ? (i) Zero (ii) Lagging (iii) Leading (iv) Unity
in transformer star connection with neutral are shorted. is there is any effect.
what is protections used for 6.6kv ht motor
what ll happen to current if two phases get short circuited
how many types of Earth bits available
Can anyone tell me what will happen if AC & DC supply get mixed???
Whether the Dc motor Droping the power factor like AC motor if lot of motor running in factory is it necessary to connect capacitor bank
Explain the function and difference of Restricted earth fault, simple earth fault and sensitive earth fault with connection diagram.
Define de-sensitivity?
what is the importance of Partial Dischage test for Electrical Equipments
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)