how to calculate the slowness and fastness of energy meter if we have different kw load for example (0.746 kw and meter rev constant 400 and we calculate the 2 rev in 30 sec) please explain the formula thanks
Meter rev constant means rev/ kwh ? Then one rotation =60x60/400 or 9kws . 2 rotations = 18kws.Time taken is 30s. Then the av load is 18/ 30 or 0.6 kw
| Is This Answer Correct ? | 2 Yes | 2 No |
how we can explain arc heatng?
how to check IR values in alternator winding?
what was the function of the auxillary relay?
Pl. brief about break-down maintenance of machine tool.
A 7 storey building has a floor area of 35,000sq.ft on each storey. On the ground floor 11KV electrical sub-station is to be erected. A load of 3kw for every 400sq.ft (p.f is 0.8) is proposed for each floor. fire pump 7.5hp, water pump 5hp, lift 2 nos, each 10hp and 20shop load of each shop is 5kw. calculate a. load each floor b. total load of building c. L.T feeders for aech floor and from transformer to main. d. distribution diagram e. capacity of sub-station/capacitor bank f. line diagram
What will be the diameter of pipe between conservation tank and transformer
what is the current density of copper & alluminium.
selection of conductor in different voltage?
in three 3.5 core aluminium ug cable. one cable is used for one phase by shrting R,Y and B wires and other 2 cables used for Y and b phases. balace 3 neutral wires are made common and connected to load. suddenly neutral current was more than line current what is the reason behind this?
Which of the following can be operated at higher frequencies ? -SCR -MOSFET -IGBT
why supervision relay is used in incoming feeders?
There are two nos of 33Kv/11Kv 5MVA transformers conecting through HT cable from substation having metering at substation itself.One transformer used at a time another remains stand by.Further 11 nos of 11Kv/440V transformers are attached on it and each transformer is having its own Power factor correction panel.Now one 33/11Kv transformer at no load condition/Stand by condition is having power factor in leading side upto 0.21 and while when another tranformer at same situation have power factor in lagging 0.42. Now one thing is clear that transformer one is having 1.5 Km long 33kv cable due to that PF goes in leading side and another is having only 250 mtr length remains him lagging. Now i want to know that how i can maintain the Power factor at no load/ stand by position though both are behaving in seperate manner.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)