Is it really necessary to have reactive power in transmission line to transfer the power from one place to other?
Answers were Sorted based on User's Feedback
Answer / e.subhash
YES very important, reactive power is playing in transmission line for transmission the active power from one place to another place.
| Is This Answer Correct ? | 4 Yes | 2 No |
Answer / e.subhash
Yes very important , reactive power in transmission line it playing very well in long transmission line. it is transmite the active power from one end to another end
| Is This Answer Correct ? | 3 Yes | 2 No |
there are two main reason for the need of reactive power.:
(1)Reactive power is needed to control the voltage level in transmission line.so If the voltage drops or become zero(because of no reactive power), the current must be increases in order to maintain the same power.If the current is too much then their is a failure of insulation for which the transmission lines go off line.
(2) IF there is less or no reactive power in the line then the generators, motors, transformers connected with the line will not work ,because they need reactive power for magnetization,hence the power will not transmitted.
Nowadays,there is a HVDC transmission which does not require reactive power to transmit,but it is needed in converters,solid states devices,semiconductors ,inverters..
| Is This Answer Correct ? | 0 Yes | 0 No |
what is function and advantage of double delta winding in induction generator?
What is the unit of inertia constant of rotating machines? Which has more inertia constant between turboalternator and hydroaltermanor and why?
how can service sitting be setted for MCCB?Example for sittings IR (CURRENT RATING),IS(CURRENT STARTING)IO (current operating)?
What is meant by the KA-rating of a circuit breaker? In this regard, discuss the stresses experienced by the circuit breakers
what is the difference between bus-coupler and bus-riser
Capacity of circuit breakers all types
Dear Friends, I have a 500KVA transformer supplying whole factory having 3 phase and single phase mixed loads. Power room has ammeters connected via CTs for individual phase. Now I know that readings shown on meter for each phase say R,Y and B are line currents. But when I want to know the total on transformer do I need to add the currents of all three phases readings shown on meter or value for anyone phase will give me the correct power load on transformer for that point of time. 2. If ammeter shows unbalanced readings for R,Y, B phases say 150, 250 and 300 respectively so can I assume that 150A i.e average of 3 will be the 3phase load currents and remaining will be 1phase currents. Please clarify my doubt.
In batteries after completion of charging which colour gas is emitted from it?
Why HT 11 KV Slipring Motors are connected in star ?
why does not tester light up when it is touched to neutral of 3 pin socket.
if we convert watt into kva,which one formula use by us,pls tell me?
different between circuit breaker & switchgear & relays
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)