why does not tester light up when it is touched to neutral of
3 pin socket.
Answers were Sorted based on User's Feedback
Answer / ankamsreekar
The practical line testers are works for the voltages above
150v. The return path is earth (land surface) via human body.
When you touched to line the voltage across the tester is
230v. If you touched to neutral the voltage across the
tester is in order of 2-10V depending up on the conditions
of distribution transformer.
so the tester will not work.
Is This Answer Correct ? | 10 Yes | 2 No |
Answer / jaswinder singh
Tester always lights up due to potential difference between
phase and earth. Neutral is at zero potential from earth so
the tester does not glow.
Is This Answer Correct ? | 10 Yes | 4 No |
Answer / k.prakashchandra
I gave the wrong answer as the word 'not' escaped my
notice..The tester requires at least 40-60 volts to light
up depending upon the series resistor used.As neutral is at
almost zero potential from ground ,tester does not light up.
Is This Answer Correct ? | 5 Yes | 2 No |
What are the components of feedback control system?
What is a advantage of Self Reset Lockout ? On Fault breaker get trip & fault no longer exist then self reset lockout how inform us?
What is meant by earthhing of a magnetic flow meter and when to use empty pipe detection?
dear friends, we are use 130 hp load run with 0.98 power factor ( 38KVAR capacitor connected ). if we need improve the the power factor to 1 (unity). how much kvar capacitor to be add. have any formula? please share with me.
what is the safety of voltage power transformer(2250KVA0
Explain how you intend to work under pressure to meet up with deadline target?
What is the general power consumption rating of CPU CRT type and Flat type, Monitor,Printer, projector, Scanner?
what is dol starter
Explain Circuit Breaker Trip Characteristics in detail.
when running 2 nos 450kva dg sets in parallel operation ,in one Dg set power factor and Kvar going to lagging and ampere suddenly going high,please give me suggestion to correct the same.
What are the causes of having an rmu explode after installation? And how do u treat the bushings of an rmu?
How can we estimate Gen rotor current?