Dear Friends,
I have a 500KVA transformer supplying whole factory having
3 phase and single phase mixed loads. Power room has
ammeters connected via CTs for individual phase. Now I know
that readings shown on meter for each phase say R,Y and B
are line currents. But when I want to know the total on
transformer do I need to add the currents of all three
phases readings shown on meter or value for anyone phase
will give me the correct power load on transformer for that
point of time.
2. If ammeter shows unbalanced readings for R,Y, B phases
say 150, 250 and 300 respectively so can I assume that 150A
i.e average of 3 will be the 3phase load currents and
remaining will be 1phase currents. Please clarify my doubt.
Answers were Sorted based on User's Feedback
Answer / ahmadmukhtiar
1. The load of R, Y or B will be the total load on
transformer.
2. There must be phase balancing system for protection
otherwise the equipment connected as load will get damaged
if all three phases are unequal.
Is This Answer Correct ? | 1 Yes | 0 No |
Answer / k.prakashchandra
Calculate load(KVA) on each phase and add
Is This Answer Correct ? | 1 Yes | 0 No |
Answer / sakthivel
each phase you find consuming power with use ammeter reading
and volt meter reading
each phase you regulate the load current or equal load
current load you choose
Is This Answer Correct ? | 2 Yes | 2 No |
Answer / abdul karim
If you wants to know the total load of transformer , you must use a watt metrer , OR you will calculate the load in watts of every individual phase then sum of all three phases will be your answer.
Is This Answer Correct ? | 0 Yes | 1 No |
The armature of shunt dc motor has 0.8ohm resistance and motor is to run on 120V circuit.If motor is suddenly thrown on circuit while armature at standstill then current drawn by motor will be??Also back emf in normal running is 110V
what should be the no load current for 3 phase ac motors ranging from 5 kw to 1000kw?
why core losses and copper losses does not depend on power factor?
what formula can be apply to calculate the No of rtrand of a cable. ?
Hi, We facing one similar problem in our computers i.e we are newly constructed our design department after that shifted our computers but our computer desktop screen is vibrating. we are conducted our electrical maintainance person he told that is UPS problem, then we changed the UPS also again we are facing that problem in that room only. then we put lcd monitors that problem is solved. But in other monitors why the computer desktop screen is vibrating please give a suggestion to me. Regards, Raju.N.G
difference between ceiling fan
24 Answers Altius Technologies, Raisoni, TCS, Uni Deritend,
how to calculate efficiency of voltage and current controlled welding transformer?
What is the formula to calculate the size of Aluminium and copper cable?
What types of I/O have you designed? What were their size? Speed? Configuration? Voltage requirements? Process technology? What package was used and how did you model the package/system? What parasitic effects were considered?
why dc exicitaion used in ac motor....?
how can you prove that in CE configuration a transistor has 180 degree phase shifted output
An alternator is started without excitation then how much voltage it will produced at strating at full rpm??