Dear Friends,
I have a 500KVA transformer supplying whole factory having
3 phase and single phase mixed loads. Power room has
ammeters connected via CTs for individual phase. Now I know
that readings shown on meter for each phase say R,Y and B
are line currents. But when I want to know the total on
transformer do I need to add the currents of all three
phases readings shown on meter or value for anyone phase
will give me the correct power load on transformer for that
point of time.
2. If ammeter shows unbalanced readings for R,Y, B phases
say 150, 250 and 300 respectively so can I assume that 150A
i.e average of 3 will be the 3phase load currents and
remaining will be 1phase currents. Please clarify my doubt.
Answers were Sorted based on User's Feedback
Answer / ahmadmukhtiar
1. The load of R, Y or B will be the total load on
transformer.
2. There must be phase balancing system for protection
otherwise the equipment connected as load will get damaged
if all three phases are unequal.
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / k.prakashchandra
Calculate load(KVA) on each phase and add
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / sakthivel
each phase you find consuming power with use ammeter reading
and volt meter reading
each phase you regulate the load current or equal load
current load you choose
| Is This Answer Correct ? | 2 Yes | 2 No |
Answer / abdul karim
If you wants to know the total load of transformer , you must use a watt metrer , OR you will calculate the load in watts of every individual phase then sum of all three phases will be your answer.
| Is This Answer Correct ? | 0 Yes | 1 No |
hi frnds...pls send me aptransco previous papers .....pls..pls,,,(madhar.rocking@gmail.com)and suggest me some websites
Why we are mostly using a single 3-phase transformer instead of three 1-phase transformers?
sent to a site and asked to explain how you would like a twenty seven flour building should be supplied with lighting and sockets plus a water boiler.
Why only three phase power generation are load are used
Write a note on materials used as a fuse element.
What is difference between Dy11 & Dyn11 vector group transformer. Can both these transformers operate in parrallel.
This is about the recent problem that we have faced in our project site. We have 6/7.5 MVA. 66/11kV three phase star - star power transformer. The neutral was solidly connected to the earthing mat. But because of high resistance of earthing mat (130 ohm on LV and 180 ohm on HV), one day LV side neutral earthing conductor melted and we had a huge damage. Can any one plz tell me what might happen when we connect power transformer neutral to the earthing mat which has high resistance (>100 ohm ) ?????
explain which quantities change in the starting and the and the running condition in induction motor
How to calculate capacitor bank value to maintain unity power factor with some suitable example?
salam, hi, how to calculate british temperature unit (B.T.U)?
what is the working principale of air circuit breaker ?
I want to know all basics of electrical engineering
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)