Dear Friends,
I have a 500KVA transformer supplying whole factory having
3 phase and single phase mixed loads. Power room has
ammeters connected via CTs for individual phase. Now I know
that readings shown on meter for each phase say R,Y and B
are line currents. But when I want to know the total on
transformer do I need to add the currents of all three
phases readings shown on meter or value for anyone phase
will give me the correct power load on transformer for that
point of time.
2. If ammeter shows unbalanced readings for R,Y, B phases
say 150, 250 and 300 respectively so can I assume that 150A
i.e average of 3 will be the 3phase load currents and
remaining will be 1phase currents. Please clarify my doubt.
Answers were Sorted based on User's Feedback
Answer / ahmadmukhtiar
1. The load of R, Y or B will be the total load on
transformer.
2. There must be phase balancing system for protection
otherwise the equipment connected as load will get damaged
if all three phases are unequal.
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / k.prakashchandra
Calculate load(KVA) on each phase and add
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / sakthivel
each phase you find consuming power with use ammeter reading
and volt meter reading
each phase you regulate the load current or equal load
current load you choose
| Is This Answer Correct ? | 2 Yes | 2 No |
Answer / abdul karim
If you wants to know the total load of transformer , you must use a watt metrer , OR you will calculate the load in watts of every individual phase then sum of all three phases will be your answer.
| Is This Answer Correct ? | 0 Yes | 1 No |
How would we calculate the no of earthing pits required for motor /panel
5 Answers APGenco, National Engineering Industries, Practical Viva Questions,
how many types of ct retio
how we sesign the transformer give some specifion regarding design of transformers
what is the difference between neutral
what do u mean by bus bar?
How open delta used for protection?
How we calculate the size of H.T cable for any transformer & rating of busbar for any L.T. panel?
what is harmonics?
During Starter Panel Com missing I Found The Main Incomer 40Amp MCB 10KA Trip When Motor Change Star To Delta Motor Rating 20HP BUT When We Use Same MCB To Other Motor It Does Not trip Or What Is Necessaries for Star Delta Starter MCB SFU MPCB OR MCCB And What are The Breaking Capacity of MCCB in the Motor above 15HP
we use Dyn11 trafo for distribution purpose, if it`s possible for replacing Dyn1. if it`s change means what will happen?
any one have papers of hpcl or sailof ELECTRICAL ENGG.
difference between turns ratio and transformation ratio?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)