Where should we terminate the shield and why?
Answers were Sorted based on User's Feedback
Shielding reduces electrostatic or capacitive coupled electrical noise in signal or communications cable
Electrostatic or capacitive coupling is proportional to the capacitance between the noise source and the signal wires. The magnitude of the interference depends on the rate of change of the noise voltage and the capacitance between the noise circuit and the signal circuit.
Electrostatic noise can be addressed by installing an electrostatic shield (also called a drain) around the signal wires. The currents generated by the noise voltages prefer to flow down the lower impedance path of the shield/drain rather than the signal wires.
The shield/drain must be of a low resistance material such as aluminum or copper. For a loosely braided copper shield (85% braid coverage), the screening factor is about 100 times or 20 dB. For a low resistance multi layered screen, this screening factor can be 35 dB or 3000 times.
The shield should be insulated to prevent inadvertent contact with multiple ground points, which could result in circulating currents.
The shield should never be left floating because that would tend to allow capacitive coupling, rendering the shield useless.
A single point connection to ground attempts to minimize the possibilty of ground-loop current that will flow between grounds at different potentials. A shield grounded at both ends can form a ground loop which can cause a processor to fault if those grounding points are at different potentials.
Vendors may specify grounding the shield at either the field end or the receiver end. When the shield/screen is grounded at one end only, the grounding is usually made in equipment panel/cabinet at the end with the power supply or the receiver. The field device end is left ungrounded and the shield/screen insulated.
At sites with equipotential grounding where the grounding is the same potential between grounding points, some vendors (Profibus DP's RS-485) recommend grounding the shield at both ends.
Cabling that runs through intermediate junction boxes shall have the integrity and continuity of shield connection maintained in the junction box without connecting the shield to a ground in the junction box.
The signal wire shield is never connected to the common side of a logic circuit (this would introduce noise into the logic circuit).
For high frequency RF noise rejection, a capacitor is inserted in series between the shield's drain wire and the ground connection.
For some communication network cables, the shield connections are unique to the particular cabling system. In some such cases, a dc short to ground is not needed because a low-impedance ac path to ground and a high-impedance dc path to ground are provided internally at each node. Follow the specific instructions in the publication provided for the specific communication network cabling system.
At any shield grounding connection, do not strip the shield back any further than necessary to make a connection.
Carl Ellis
Measure First
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / praful lilhare
on Power supply side we should terminate but i dont know why?
| Is This Answer Correct ? | 1 Yes | 0 No |
If a control valve is hunting means means if we are giving 50% to the cv, the cv will open at 51% then slowly slwoly it will reaches 49% , then it will reaches again 50%, this type of action occured frequntly.. so what to do for solve this problem. The possible cause is in volume booster or positioner's relay.. positioner is double acting .. and make siemens..sipart.The cv is double acting and mounted for anti surge operation, it having 4 nos. volume booster, one sov, one positioner, etc..?
2 Answers Gujarat Fluorochemicals Limited (GFL), Shell,
what is the formula for changing Range of Transmitter from X mmwc to some Y mmwc with respect to DCS NCMH flow range from x NCMH to y NCMH?
any one can send me instrumentation previous interview papers? I prepare for MNC Company Interviews? my mail id- Rakesh.Golla@dodsaldxb.ae , and another mail rakesh.gvk@gmail.com
What is the use of double seated valve?
generally transmitter power supply having some range(12v to 35v) but the out put(4-20 mA) must same for given input.If we vary the power supply voltage then output mA also to be change according to V=IR. Is there any voltage regulator in the transmitter ?
what happens when the profibus fails while in operation (operation of a valve)?
I installed the smartplant instrument v8, but can not be opened, that always said: "INTools 2007 hardlock no found". So Could you help me how to do for that?
Hi buddies! i am facing a problem and if someone could help me it will be an immense pleasure to me. we have compect logix PLC 1769 2L AO module to Heat @ 52 to 56 Deg C .So if anyone can do please help me out with this problem.I'll be highly grateful.
What is difference between magnetic flow transmitter & Electromagnetic flow transmitter?
what difeerent between HART and BRAIN?
What is super thermocoupal?
What is the meaning of Feedback? How many types it is? Explain it?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)