Where should we terminate the shield and why?
Answers were Sorted based on User's Feedback
Shielding reduces electrostatic or capacitive coupled electrical noise in signal or communications cable
Electrostatic or capacitive coupling is proportional to the capacitance between the noise source and the signal wires. The magnitude of the interference depends on the rate of change of the noise voltage and the capacitance between the noise circuit and the signal circuit.
Electrostatic noise can be addressed by installing an electrostatic shield (also called a drain) around the signal wires. The currents generated by the noise voltages prefer to flow down the lower impedance path of the shield/drain rather than the signal wires.
The shield/drain must be of a low resistance material such as aluminum or copper. For a loosely braided copper shield (85% braid coverage), the screening factor is about 100 times or 20 dB. For a low resistance multi layered screen, this screening factor can be 35 dB or 3000 times.
The shield should be insulated to prevent inadvertent contact with multiple ground points, which could result in circulating currents.
The shield should never be left floating because that would tend to allow capacitive coupling, rendering the shield useless.
A single point connection to ground attempts to minimize the possibilty of ground-loop current that will flow between grounds at different potentials. A shield grounded at both ends can form a ground loop which can cause a processor to fault if those grounding points are at different potentials.
Vendors may specify grounding the shield at either the field end or the receiver end. When the shield/screen is grounded at one end only, the grounding is usually made in equipment panel/cabinet at the end with the power supply or the receiver. The field device end is left ungrounded and the shield/screen insulated.
At sites with equipotential grounding where the grounding is the same potential between grounding points, some vendors (Profibus DP's RS-485) recommend grounding the shield at both ends.
Cabling that runs through intermediate junction boxes shall have the integrity and continuity of shield connection maintained in the junction box without connecting the shield to a ground in the junction box.
The signal wire shield is never connected to the common side of a logic circuit (this would introduce noise into the logic circuit).
For high frequency RF noise rejection, a capacitor is inserted in series between the shield's drain wire and the ground connection.
For some communication network cables, the shield connections are unique to the particular cabling system. In some such cases, a dc short to ground is not needed because a low-impedance ac path to ground and a high-impedance dc path to ground are provided internally at each node. Follow the specific instructions in the publication provided for the specific communication network cabling system.
At any shield grounding connection, do not strip the shield back any further than necessary to make a connection.
Carl Ellis
Measure First
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / praful lilhare
on Power supply side we should terminate but i dont know why?
| Is This Answer Correct ? | 1 Yes | 0 No |
what is zero and span ?
what is the usage of QDV & VOLUME BOOSTER.
what is intrument termination what is commisioning
How many loops are there in the power plant? how many closed & open loop in the power plant ? Please give me the exact clarification?
Type of level transmitter commnly used in Procees area are the following. a.________________This type of level transmitter works as follows
Hi Friends , i need one urgent help , i am preparing for M.tech entrance examination , i need some obejective questions related to instrumentation field. where can i get those ? can anyone help me pls ?
how we are selecting instuments by differentiating certain instruments in 4 to 20 ma range and certain in 1 to 5 v dc
when an eddy current probe is installed inside of a turbine or compressor in case of probe problem same as:crash of head of probe,changing the scale factor because of low measuring gap(physical gap is ok(example=1.14mm)but voltage is reduced(example=-6 volts),is any way to check the probe,when the ohm of probe is ok.thank you,(Karim Tavakoli)
A RANGE OF TRANSMITTER IS (0-400)B mm abs what is "B"?
what is the difference between servo valve & proportional valve
How can we loop powered for a transmitter.How we can do wiring
SOME OF YOUR QUESTIONS ARE NOT MAKING ANY SENSE SO TRY AND PUT IN A LITTLE BIT MORE EFFORT BEFORE YOU POST A QUESTION. WE WILL ONLY HELP THOSE WHO WE CAN SEE ARE TRYING TO HELP THEMSELVES.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)