If we says that current is flow only when there is closed path & neutral work as a return path for the same. Then how circuit is closed in three phase as no neutral available ??
Answer / sukanta bhowmik
Not only neutral but in case of three phase system another phase act as a return path.suppose you connect a load between two phase. Now in this case current will flow from one phase to load and then another phase and in this case circuit complete through transformer from which power is feeding to the load. Means complete circuit will be ---current from one phase of transformer-->to load--->to another phase---->finally transformer.
| Is This Answer Correct ? | 7 Yes | 0 No |
can d.c.transformer exist? if yes then what its max. rating?
What do you mean by lighting transformer?
Cb closed condition if there is a tcs fail whether cb will trip or not
will we have to design the UPS differently for both i.e. if we want to connect the two batteries in parallel and/or we want to connect the two batteries in series ?
What is harmonics in AC waves. How it is generated? How it will effect the system network? how can eliminate it?
Define open loop control system.
how work the differential protection relay in details?
Why generating voltage is limited up to 22kV?
What is the distance between body earthing and neutral earthing.?
What are the advantages and disadvantages of open loop control system?
Brushed alternator is also called dc generator ? its true or false ?explain it ?
what is the current law ?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)