HOW TO CALCULATE THE WIRE SIZE FOR THE GIVEN LOAD?
Answers were Sorted based on User's Feedback
Answer / tej4fun
first calculate the full load current of ur given load
and then the continous and non continuos load it has to
carry and the length from the feeder to the load
with the length and amperage calculate the voltage drop
with this u can come to final amperage of the cable then u
can choose the respective cable from any manufactures guide
| Is This Answer Correct ? | 3 Yes | 1 No |
Answer / g v s
calculate the full load current for a given load, select
the cable from oem catalogue and then find out dearating
factor from oem or NFPA 70 TABLES .Depending upon laying
of method (whether it is under ground or o/h or both), then
multiple the df for a given load current. after this u hv
to calculate the voltage drop and it should be within the
limits as per ieee and ansi standa.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / simon peter
First of all u should know what is the amount of current of the load which will b drawn by the load.......
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / sudhir patil
By given load calculate the max. current & use standrad
gage table or normally 1SQ.MM For 1.5A Current.
| Is This Answer Correct ? | 1 Yes | 2 No |
What is the minimum distance between MV busbare (P to P & P to E) as per some standards
how can we change the rotating direction of single phase AC induction motors?
12 Answers Heubach Colour, L&T, MNM Jain Engineering College,
how many hvdc lines in india???
11 KV distribution system where neutral is produced ?
4 Answers ciss, TATA, Tata Motors,
If we impress a dc voltage of 230 V on an unloaded 230 V, 50 Hz transformer it wi A give high secondary voltage B burn out C give secondary voltage as per K D none of these
What is the formula to calculate the rating of power cable for three phase current.
how to calculate knee point voltage for pt?
IN OLTC we observed "OUT OF STEP" Alarm, we have two different transformer, when both are in parallel this type of alarm observed. what's the meaning of this alarm and why it occurs???
State magnitude criterion.
what is the VA(Voltampire)? define with calculation?
what is earthing
is that a problem if i connect a single phase load to a secondry delta connected transformer but i get a neutral from other transformer i the system?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)