why C.T protection required for H.T.lines?
Answers were Sorted based on User's Feedback
Answer / singa
CTs are having both measuring as well as protection cores.
Measuring cores:
In a HT lne, current value is in terms of few hundrest to
kilo amps. In practical these cannot be measured by meters
direclty. Hence the current in the transmission line will
be stepped down to the standard values for example 2000/1A.
THis refers to the flow of 1A at CT secondary when 2000A
flows in HT line.
Protection core: As the fault current is very high during
the time of fault, this increase in current is used to trip
the faulty section. In order to sense the fault current,
protection cores of CTs are used to feed the protection
relay.
| Is This Answer Correct ? | 7 Yes | 0 No |
Answer / suresh
actually Ct is measuring unit, according our require ment
we can take 2 or 3 core for metering and protection. for HT
lines any fault will came like LG fault we can rectify the
fault by using CT it is a High voltage to mesurement
control volatge will be step down
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / dhaval patel
While in line, if the CT terminals get open, it can result
in heavy faults in CT core. To prevent developing of such
higher voltage at the secondary terminals of the CT, it
shall be protected.
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / k.prakashchandra
And without CTs you can not measure HT current.
| Is This Answer Correct ? | 0 Yes | 0 No |
A 400KVA ,50HZ TRANSFORMER IS TO BE OPERATED AT 50HZ.THEN KVA RATING OF THE TRANSFORMER?.
What is meant by stator? What is meant by rotor?
What is the purpose of RECTIFIER ASSEMBLY in AC power generators?
Explain the working principle of Vacuum circuit breaker and Air circuit breaker
10 Answers HP, Trinidad and Tobago Electricity Commission T TEC,
Name two low frequency oscillators?
Draw the vector diagramme for Asynchronous Induction Generator at noload,half load and fullload.
How star and delta connections inherently eliminate triplend harmonics?
11 KV Power cable end earth connection insulation got burned wht is the reson pl give the resons
What is the voltage b/w nutral and earth
What are the conditions to be satisfied before connecting two DC generators in parallel?
what will happen when power factor is leading in distribution of power?
10 Answers AMET, JTO, Power Grid,
What will happen if the 50HZ Transformer is connected with 60HZ power Supply
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)