Is it possible to run HT motor through LT VFD (LT VFD supply given to Transformer LT side and transformer HT side connected to motor)
Answer / kingshuk dey
To start with, let's get our concepts correct. The motor supply comes from the VFD, which in turn is connected to the power supply from a board (or LT side of transformer, in your case).
Supply(TRF) --> VFD --> Motor
First off lets assume your VFD type is less than or equal to this LT supply. (LT/HT for TRF is subjective, Lt can be 220V when HT is 460V, or 460V when HT is 1000V etc). But a 460V VFD will burn its fuses if connected to 1000V.
Anyway, if you connect the VFD to LT side, and the motor is HT (meaning it's rated for a heavy current like 32KV), the motor will try to pull more and more current to start from the VFD, ultimately exceeding the current setting of the VFD and it will trip with an Overload or Overcurrent (OH, OC) fault on its display. If the current is enough to start the motor, it will rotate, but with very less speed (like if the motor is not connected to any load).
Just as a matter of interest, if you connect the LT side of TRF to VFD, and HT side of TRF to motor, "nothing" will happen as there is no current source (both VFD and motor are current consuming equipments) :P
Motor --> TRF HT -- TRF LT --> VFD (LOL!)
| Is This Answer Correct ? | 1 Yes | 3 No |
How Self works in DG set
2 v/500amp/hr to 1.80vpc at 20 degree celsious 2v/5ooamp/hr to 1.75 vpc at 77degree farren .this is the capacity of a battery .what is the meaning of this . can i get a detailed explenation
what are the applications of TIG welding
which course is maximum demand in industry and give me the list of best courses for electrical engineers
If i have 200 test cases and we have to execute but we don't have time to execute all testcases.within 1 hour we have to execute that testcases and prepare the test report.so how i have to resolve this problem? is there is any technique in the testing.
How to arrange a hous hold earthing system to keep minimum earth resistance( below 7ohms).
What is the ohms law?
when we increase load , current drawn from source also increases why ?
What's the differs between voltage & current & emf.
its Kva and Kv are same?
What is the loss of transformer of 220kv/11kv, 63/80 MVA and 18.05% impedance
we have two generators different capacity on 15 MW and other 6MW at 11 KV , 15 MW gen. bus short level current 40KA,and 6MW short level current 25KA,, length of cable 100MTR between 6 MW from 15MW gen. for bus coupling . kindly tell any one can we use both NGR OR one NGR from any GEN. BOTH NGR has diff. rating. Tariq pakistan
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)