While DG is on Load? we can start the capacitor bank?
Answers were Sorted based on User's Feedback
Answer / srinivasa rao talasila
We can use the capacitor while DG is on load but you should
maintain Lag PF only and any abnormal switching off of the
load means PF will shoot Up and the AVR will fail
immediately.
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / k.prakashchandra
Capacitor bank is usually connected while DG is on load.But
care should be taken to avoid leading pf which causes higher
terminal voltage.
| Is This Answer Correct ? | 2 Yes | 4 No |
Is it possible to interlock between ACB & MCCB?
HOW WE CAN REDUCE THE CIRCUIT COMPLEX OF STAR-DELTA STARTER .BECAUSE NOW WE USING ONE TIMER RELAY & THREE CONTACTOR FOR MAIN,STAR & DELTA ?IF ANY IDEAS PLZ POST.THANK U
WHAT WILL BE THE SPEED OF MOTOR IF NO.OF POLES ON STATOR ARE NOT EQUAL TO NO. OF POLES ON ROTOR.???
HOW TO DESIGN THE body EARTH cable(Copper Conductor) size for 60KVA UPS?
NOW A DAYS THE POWER SUPPLY IS VERY LOW.SO THE FLURESCENT TUBE LIGHTS ARE VERY DIM.IS THERE IS ANY WAY TO INCREASE ITS BRIGHTNESS?FOR EXAMPLE ANY CONVERTER,CONDENSER?
Why a tesa lamp is glow between two phase?
why overcurrent fault occurs in power system.
why use only sf6 circuit breker in 400 kv sub station
Minimum IR value of 1.1 kv grade 3.5c (300, 240,185,150,120,95,70,50,35,25) sqmm Aluminium XLPE cable and 4c (16, 10,6 & 4) sqmm cu arm cable between RY,YB,BR,RN,YN,BN,RE,YE,BE & NE.
what is frequancy
What is bode plot?
its Kva and Kv are same?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)