How DP Transmitter can be calibrated for crud application in floating roof tank?
Answers were Sorted based on User's Feedback
Answer / rajesh.
Compare to SAAB tank gauge measurement, DP level transmitter reading will not accurate. As the crude is viscous and it will choke up impulse tubing. It is better to install diaphragm capillary seal type Dp level transmitter. To calibrate Tx, Isolate primary valve of Hp and Lp tapping. depressurize Tx from manifold. check zero. measure the mmwc of tank and apply the value as per HP calibration.
| Is This Answer Correct ? | 4 Yes | 0 No |
Answer / prabhu
DP transmitter can be calibrated by fixing the HP tapping on the roof and make the LP as open. now measure the mm/wc of the tank and apply the value as HP for calibration.
| Is This Answer Correct ? | 0 Yes | 0 No |
thru which signal does µP communicate with memory
Why Boiler Drum level transmitter (TX) or level transmitter rang always put -600 to 0 other -900 to 0. Mines range why useā¦.?
Yokogawa CENTUMVP R6.09 unable to download to Engineering Station with ExaOPC R3.75 The issue is when I try to download the common project section to the Engineering Station (STN) from the HIS in System View, it is unable to connect. The error displayed is: WARNING: Could not connect to equalize destination. (7001) Retrying. Number of retries = 0/1 ERROR: LdXopsLoadMain: connect error 10060 ERROR: Processing terminated due to connection error. (7002) Equalization end with errors. STN0149 ---- ERROR = 2 WARNING = 1 ---- Background: >Updated the ExaOPC software on the STN from 3.60 to 3.75 >STN operating system is Windows Server 2008 R2 >HIS operating system is Windows Server 2016 Stanard Solutions attempted include: >Ensuring all IP addresses are correct and all networked devices can be pinged. >The ability to ping a device using its host name from another device (<ping STN0149> from HIS) >Ensure both devices firewalls are disabled. >The antivirus installed on the STN is disabled. >Ensuring both devices are within the same workgroup. >Added both devices to each other's Host and LMHost files. >Running IT Security tool after changing any administrative settings.
how to check control valve was passing?how to check online?
What is the cascade control
Why Bently Nevada use negative voltage for vibration probes?
How to find out the current of two motors having same power consumption but different RPM?
Speedtronic system .
What is the SCAN time of a DCS/PLC? What is the typical value for scan time of DCS and PLC?
6 Answers Essar, Gasco, Siemens,
What is the exact differences between HART,FOUNDATION FIELDBUS,PROFIBUS?
Is it possible to convert 4 wire transmitter to convert to 2 wire with additional relay.Please send detial with drawing,i will appreciate.
Yokogawa dcs normally where will change 4-20 MA to DC voltage( node or I/o cards?)
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)