under which situation or why restricted earth fault protection operates in out side its zone that is external fault
Answers were Sorted based on User's Feedback
Answer / hg
1) if any one ct saturates at through fault current due to
a) high harmonic content of current in through fault current leading to high voltage appearing across secondary and the ct saturates
2) under above scenario if there is no stabilizing resistor/ damage to stabilixing resitor than relay may operate
| Is This Answer Correct ? | 0 Yes | 0 No |
This may happen when bushing neutral ct is used for REF , as it is usually not identical to the line ct s
| Is This Answer Correct ? | 0 Yes | 0 No |
what is the defenation of efficiency in the high pressor boiler? what is the formila of efficiency in the high pressor boiler?
what is need of primary water system in power plant?
By any way can we increase the B check hours from 300 to 500
What is Droop Control in Woodward?
What is the use of NULL meter on AVR panel
How to calculate power press toneage
under which situation or why restricted earth fault protection operates in out side its zone that is external fault
explain why direct on line starting toque and current may not be acceptable
2. what is meant by exhausthood temp?
What is difference between Actual Drum Level and Compensated Drum Level?
how mony power plants in India
What is A.T.T.?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)