Answer / rich sawe
CTPT - The Current Transformer and Potential Transformer,
these are instrument transformers used mainly for high voltage instrumentation purposes at the substation
1.Measurement purposes;these transformers provides low level signals to the metering equipments to measure line voltage level and line currents at the substation.
2.Protection purpose;these transformers provides signals to the upon occurrence of fault , over-current and under-current faults are firstly sensed by the current transformers then signals the O-C/U-C RELAY to trip the Circuit breaker ,Over-voltage and under-voltage faults is firstly sensed by Potential Transformer then signals the O-V/U-V RELAY to trip the Circuit breaker.
3. The occurrence of unbalanced fault condition in three phases at the substation is detected by the current transformers and potential transformers and the signal is fed to the respective relay to operate the circuit breaker.
4.on the POWER GRID the performance and operating status of the HIGH VOLTAGE SUBSTATION are monitored and controlled through feedback from CTPT
...DIT TANZANIA...
| Is This Answer Correct ? | 7 Yes | 2 No |
Construction of Diesel generator set?
which INDIAN STANDERD in Mention the earth test value?
What is a neutral
4 Answers Adani Ports, Dr Reddys,
Is it possible to obtain 480v or 550v in single phase output by giving the input to 230v to a single phase torodial type transformer without using a stepup transformer?
If I want to replace a 26KW Slip ring Motor with a Squirrel Cage motor & Drive (for a Hoist Application). How can I approximate the Motor & Drive HP required in new Setup.
Impedance relay is directional relay or non directional relay?
In EDO ACBs what is a purpose of closing coil and motor, what is the operation of these devices are they inetconnected. means if we give supply to motor and by BCS we charge Closing coil,what exact is operation is and how it charge a spring of ACB. Sir if anybody has an wiring diagram please send me the link to operate and EDO breaker.
how can calculate static 3phase 4wire CT & PT operated energy meter constant when calibrating using refference meter suppose we have 11kv/110v PT and 30/5A CT, the meter constant is 160imp/kwh, where meter is showing MW energy? give me solution which constant i feed in my refference meter for calibration of energy meter?
Spacing of Transformers ratings are 10kva,15kva,25kva,63kva,110kva,150kva .........so on Q) Why transformer are not manufactured having ratings in between or other than these standard ratings ?
what do u understand about FACTS? how they are useful?
what are upstream faults and downstream faults in power system
what are the main Parts of VCB
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)