what is work of CTPT in 33/11kv Substation
Answer / rich sawe
CTPT - The Current Transformer and Potential Transformer,
these are instrument transformers used mainly for high voltage instrumentation purposes at the substation
1.Measurement purposes;these transformers provides low level signals to the metering equipments to measure line voltage level and line currents at the substation.
2.Protection purpose;these transformers provides signals to the upon occurrence of fault , over-current and under-current faults are firstly sensed by the current transformers then signals the O-C/U-C RELAY to trip the Circuit breaker ,Over-voltage and under-voltage faults is firstly sensed by Potential Transformer then signals the O-V/U-V RELAY to trip the Circuit breaker.
3. The occurrence of unbalanced fault condition in three phases at the substation is detected by the current transformers and potential transformers and the signal is fed to the respective relay to operate the circuit breaker.
4.on the POWER GRID the performance and operating status of the HIGH VOLTAGE SUBSTATION are monitored and controlled through feedback from CTPT
...DIT TANZANIA...
| Is This Answer Correct ? | 7 Yes | 2 No |
How to calculate voltage drop in copper and aluminium cable? I have laid 240Sq.mm Aluminium cable for the length of 600 Mtrs in 1 Mtrs underground. Normal load is 150A. Transformer is 630KVA, 6.KV/433V. But, I am getting only 395 Volts when load. How to calculate voltage drop and what is the permissible voltge drop for this circuit?
Why do we avoid electrical conduits in floors at apartments?
lenz law application and define
EARTH AND NEUTRAL ARE JOINTED OR NOT?
which type of amplifiers are used in multimete?
control diagram of star delta starter
what is the physical connection of a analog i/p to a analog i/p module (ab plc)and through a analog o/p module(ab plc) to a analog o/p . and how all the process control by scada
what is meant by Hrc fuses.?In the distribution system different rating hrc fuses are used for tranformer(which is 3k,6k,10k,15k etc).what is k?.plz any brother tell me about k?
We have 11kV/110V three phase indoor potential transformer in 66/11kV Sub-station, where the failure of PT is frequently happening and the rating of the PT is 0.2 class accuracy, with primary star and seconday (two cores) star connected. Some experts has suggested to not to connect the PT Primary neutral to the ground because when transformer neutal NCT connection is loose; the faulty current will flow through the PT primary neutral, resulting into failure of PT. My question is: Is it necessary to remove the primary neutral connection of the PT from ground? if not, what would be the reason for failure of PT. Please guide me.
how to convert lv line to hv line and viseversa, any losses will occur during this process
is there any difference between inverter and a battery
In India which type of PLCC IS used?
2 Answers Cipla, Ford, Jayashree,
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)