Answer Posted / rich sawe
CTPT - The Current Transformer and Potential Transformer,
these are instrument transformers used mainly for high voltage instrumentation purposes at the substation
1.Measurement purposes;these transformers provides low level signals to the metering equipments to measure line voltage level and line currents at the substation.
2.Protection purpose;these transformers provides signals to the upon occurrence of fault , over-current and under-current faults are firstly sensed by the current transformers then signals the O-C/U-C RELAY to trip the Circuit breaker ,Over-voltage and under-voltage faults is firstly sensed by Potential Transformer then signals the O-V/U-V RELAY to trip the Circuit breaker.
3. The occurrence of unbalanced fault condition in three phases at the substation is detected by the current transformers and potential transformers and the signal is fed to the respective relay to operate the circuit breaker.
4.on the POWER GRID the performance and operating status of the HIGH VOLTAGE SUBSTATION are monitored and controlled through feedback from CTPT
...DIT TANZANIA...
Is This Answer Correct ? | 7 Yes | 2 No |
Post New Answer View All Answers
a 100mva,400/200v transformer has leakage impdce of 10% draws a steady state line currentof---------------
how can i determine the KVA/MVA rating of transformer precisely?? is there any standard test?????
What are the main advantages of bode plot?
what is two point starter?
What is the percentage loss for aluminium wire for HT line more than 11KVa
what's the difference between 'shaft power demand' and 'BHP' , when we consider electrical load list.
To make a basic instrumentation amplifier, it takes A One op-amp with a certain feedback arrangement B Two op-amp and seven resistors C Three op-amps and seven capacitors D Three op-amps and seven resistors
How will you utilise electrical power? You can start from the generating station.
why it is so called as xlpe(cross linked poly ethyline) cable?
What are the site acceptance tests for power cables, DG Sets, LT panels & 30kVA UPS ?
why the active power flow of some line is increased when the active power of out is cut ?
hi frnds what is meant by harmonics & what is meant by third hormonics,where its will occur ?thank u
Why use in ht motore
What should be the height of basement according to NBCC code?
What is the difference between voltages or potential difference? And what are they?