why we are using ungrounded RTD sensor and what is difference
between grounded RTD and Ungrounded?
Answer / carl_ellis
Show me a 'grounded RTD'. I have never seen a commercial
grounded RTD. The probability of a measurement error due to a
ground loop is too high.
An RTD measurement requires a stable, constant current
source, which is generated by the sensing circuit. If an RTD
element were grounded, a ground loop could affect the current
source depending on the difference in ground potentials at the
RTD element and the sensing circuit. That would create an error
in the measurement.
Grounded thermocouples work some of the time, but other
times some form of isolation is needed because of a ground loop
issue with a thermocouple.
You use ungrounded RTDs because that's the best way for them
to function.
Carl Ellis
Measure First
| Is This Answer Correct ? | 4 Yes | 0 No |
how to install Differential pressure transmitter in gas line.i need transmitter down side.
tell me the field & lab calibration procedure step by step with diagram of pressure gauge, pressure switch, pressure transmitter, temperature switch, level switch, flow switch, flow transmitter, temperature transmitter, temperature indicator, flow indicator, level indicator, control valve, thermocouple, pressure indicator (digital & analogue),
what is pressure control
1 Answers GNFC, IBM, Privi Organics,
why we use 4-20 mA for calibration of the instruments.why we cant use 0-20 mA?
can you send remote seal interface level transmitter calculation steps for oil water saperator.
0 Answers Sasol Firm, Thermax,
in control valve is constructed as per API 6D or API 6A, then which standard is used for fire testing of valve?.
what is power factor?
what is DCS and SCADA?
we callculat main steam flow by D.P. but where is H.P. & L.P. IN Orfics?
Calculate the maximum pressure drop that can be allowed to occur across a control valve, so that we can prevent cavitation / flashing from occurring. Use the following formula: Δ P allow = Km (P1 – PvapourA) where, Δ P allow - the maximum allowable differential pressure for sizing purposes, or terminal pressure drop; Km- the valve recovery coefficient from the manufacturer’s catalogue; P1 - absolute inlet fluid pressure; PvapourA - absolute fluid vapour pressure at the inlet temperature; Use Atmospheric pressure = 101.3 kPa, P1 = 1200 kPa(g), PvapourA = 4 kPa, KM = 0.72
how many type of plug are used in pneumatic control valve,name them.
What is negative range in transmeter?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)