10Hp, 3-phase, 415v, 50Hz induction motor.
The above motor is to run on Star-Delta connection, so how
do i make following hardware selection
1) MCB, 2) Contactor, 3) Wire Gage (Depending on P-P current
or Line Current), 4) OLR,
Please tell in detail how to do the above, so as to get the
ans. of it even if the Hp rating changes.
10 hp=7.5 kW. The manufacturer has to indicate the starting
current.
Let's say the motor is designed for star/delta starting
then according to IEC 60034-12 Tab2 for 6.3 kw up to 25 kw
S1=12 then maximum permissible starting current will be
Istart=12*7.5*1000/1.73/415=125.2 A.
The short-circuit protection has to be set at
1.25*125.2=156.5 A.
The circuit breaker rating has to be 150 A. The motor
overload has to be set at 1.25*Irated and also will trip
the breaker if the current of 2*Irated will last more than
the permissible stall time [let’s say 4 sec].
The supply cable allowable current [see IEC 60364-5-52]
shall be 1.25*Irated.
Usually a 7.5 kW motor at 415 V rated current will be 13-16
A then the cable permissible minimum should be 20 A.
According to the above mentioned standard 2.5 mm^2 copper
conductor PVC insulated will be ok.
You have to check the voltage drop also: no more than 3%
rated and 10% at start. If DV=1.73*I*[R*cos(fi)+X*sin
(fi)].R,X =total resistance-at 70 dgr.C- and reactance
[ohm].
cos(fi)=0.85 [approx.] rated and 0.3 at start. Sin(fi)=
(1-cos(fi)^2)^0.5.
In this case if the cable length will be 80 m 4 mm^2 copper
conductor has to be employed.
| Is This Answer Correct ? | 6 Yes | 0 No |
how does calculate loss correction factor in transformer
If a earth leakage circuit breaker trips is it possible to tell which house circuit breaker (I have four) is the faulty circuit?
IF DISTANCE IS 100METERS B/W AMP.METER AND CURRENT TRANSFORMER WHAT WILL BE AFFECT IN ACCURACY .METER CAN SHOWING ACCURATE CURRENT OR NOT IF NOT WHAT CAN I DO TO GET 100% ACCURACY.
How to know of any cable size if there are not written on cabl?
what is meant by power factor ?
WHY IS THE NO LOAD CURRENT SMALL FOR A TRANSFORMER COMPARED TO OTHER ROTATING ELECTRICAL MACHINES??
1ampear me kitna watts hota hai aur elcb ka pura naam kya hai
18 Answers Al Khayyat, Alpha G, BEC, Bhel, CGS, Electrical, Fiem, Firmenich, HLG Habtoor Leighton Group, Jash, Kandia, Maruti Suzuki, Minda, NTPC, ONEIC, Pace Process Controls, SMTC, SR, Sunrise Electrical, Sushil Enterprises, Suzlon, Voltage,
When calculation of fault current and fault Kva is to be done,why always we use per unit value and why we consider the base kva?
can we run a motor rated 50Hz,415vac,1440RPM At higher speed then rated on name plate with the help of VFD /drive on long term basis.wheater it will effect the motor life
what will happen at the time of CT saturation?and what will be the Relay's function at the time of CT saturation?
what are fluorescent lamps (fluorescent fixtures) & what are incandescen lamps (incandescents fixtures) ? differences between these two ?
Which is remain unchanged in transformer action?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)