10Hp, 3-phase, 415v, 50Hz induction motor.
The above motor is to run on Star-Delta connection, so how
do i make following hardware selection
1) MCB, 2) Contactor, 3) Wire Gage (Depending on P-P current
or Line Current), 4) OLR,
Please tell in detail how to do the above, so as to get the
ans. of it even if the Hp rating changes.
10 hp=7.5 kW. The manufacturer has to indicate the starting
current.
Let's say the motor is designed for star/delta starting
then according to IEC 60034-12 Tab2 for 6.3 kw up to 25 kw
S1=12 then maximum permissible starting current will be
Istart=12*7.5*1000/1.73/415=125.2 A.
The short-circuit protection has to be set at
1.25*125.2=156.5 A.
The circuit breaker rating has to be 150 A. The motor
overload has to be set at 1.25*Irated and also will trip
the breaker if the current of 2*Irated will last more than
the permissible stall time [let’s say 4 sec].
The supply cable allowable current [see IEC 60364-5-52]
shall be 1.25*Irated.
Usually a 7.5 kW motor at 415 V rated current will be 13-16
A then the cable permissible minimum should be 20 A.
According to the above mentioned standard 2.5 mm^2 copper
conductor PVC insulated will be ok.
You have to check the voltage drop also: no more than 3%
rated and 10% at start. If DV=1.73*I*[R*cos(fi)+X*sin
(fi)].R,X =total resistance-at 70 dgr.C- and reactance
[ohm].
cos(fi)=0.85 [approx.] rated and 0.3 at start. Sin(fi)=
(1-cos(fi)^2)^0.5.
In this case if the cable length will be 80 m 4 mm^2 copper
conductor has to be employed.
Is This Answer Correct ? | 6 Yes | 0 No |
if the length, number of turns and area of coil are doubled then inductance of the coil becomes.?
can indirect loading be called as phantom loading?
Reason of secondary of ct always short
why we generate transmit and distribute electrical supply in multiple of 11
wht is this amps in power consuption and how can we convert that into consuption hours ? i am a sales executive of a energy saving lamps .
what are problems caused by the pdu in rack server
Why we does earthing for transformer neutral point
WITCH CARDS IN USE IN FIRE CONTROL PANEL.
what is meaning of AMF, WHY IS USING IN GENSET
how to identify the cable quality and what is flame proof cable
Whats changes in Transformer Oil BDV in changes in temp or Climate?
why odd hormonics only will effect the power system.why not even hormonics