How to Calibrate Level Troll in field
If a differential pressure transmitter is calibrated for 0~2500 mmH2o and transmits a 4~20mA dc signal. The transmitter is placed across an orifice plate which is sized to create 2500 mmH2o differential at 5000m3/Hr a) what is the flow rate when the transmitter signal is 13.0mA DC? b) what is the signal output of the transmitter when flow rate is 2500 m3/Hr ?
How you calibrate absolute pressure with the calibration range of 0 to 1000 0C Absolute. Please explain the procedure for calibration.
Full form of KKS when use DCS.
What is the minmum distance between the electrical panel and Instrument panel
what is differance between SOE an alarams
What is the IEC Standard for PLC I/O Terminal wiring Procedure?
In your own words, would you expect an ultrasonic level device to work better in a pressure vessel with a high pressure or a strong vacuum, and why?
How to calibrate DP tramitter in flow measurement application? consider my range of flow is 0 to 2000 kg/hr ? please give calculation of , How much pressure applied on low pressure side and high pressure side please give detail of calculation .... It so important for me please reply as soon as possible
What is the exact differences between HART,FOUNDATION FIELDBUS,PROFIBUS?
i want the equation of this question. Tranmitter range is 120 mmwc and dcs flow range is 1700 nm3/hr. if i want to change dcs range from 1700 to 2400 nm3/hr then how much dp i have to enter in transmitter
Which is your favourite subject & explain any one topic of it.
units for vibration in power plant