in plc source and sink meaning?
Answer / mugil
Assuming 24 vdc I/O cards.
On a transistor output card Sourceing is PNP or Active High. This means that you connect the output to the + side of the load device and connect the other side to 0vdc. If the output Card is Sinking it is NPN or active low meaning that you would tie the + side of the device to 24vdc and the common would connect to the output card.
On input cards if the input card is a sourceing card you would use NPN sensors. The cards common connection would be to a +24vdc source and the device (sensor) would give a path to 0vdc. If the input card was sinking you would use PNP sensors. The sensor would be connected to the + 24vdc source and the output from the device would connect to the PLC input card which would have a common connection to 0vdc.
| Is This Answer Correct ? | 0 Yes | 1 No |
what is hot loop check and cold loop check.
3 Answers Bapco Bahrain Petroleum Company,
what is the difference between CPC and i/p converter
What is BMS (Building Managment System)& is AHU / HVAC are in BMS.
draw shematic diagram of c/v positioner(smart type)?
pt range is -45 psi to 45 psi.friends can you give answer with calculation and with linerity scale like 0%,25%,50%,75%& 100%?
How will you measure surface temperature of SUN?
How to consider the flow directions for control valve (Globe) Is the there any easy understanding in order to select the flow directions?
WHAT IS SMART SENSOR AND DIFFERENT B/W SMART SENSOR AND SENSOR??? PLS GIVE ME ANSWER AS SOON AS POSSIBLE.....
How does SmartPlant Instrumentation interface with physical design (3D modeling)?
basic connection and principle of axial shift sensor n differential sensors in tubine describes n draw......
Type of level transmitter commnly used in Procees area are the following. a.________________This type of level transmitter works as follows
When a timer is placed in RS Logix 5000 with preset value less than its scan time it is malfunctioning. i.e., if the preset is set to 30ms still the timer TT bit is counting till 150ms(its scan time). Any solution for the problem?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)