Dear all... I have 1 0-400 duplex type RTD, I connected the
A side to the temperature indicator and B side to the PLC
panel, but when I have observed then found that The PLC side
temp has the variation. and it was distub to other RTD temp
also. so what can I do.pls help me
Answer / carl_ellis
An offset in readings from separate RTD's can indicate
- a difference in calibration of the analog input devices
- a bad RTD element, one that has drifted out of spec
- a common ground issue with ground loops between the analog
input devices
An RTD is supposed to be ungrounded and the two RTD's in a
duplex element are supposed to be electrically isolated from
one another, so it is unlikely the ground loop is unlikely
unless poor wiring of the extension wire or head wiring has
created a connection to ground.
If you're complaining about a small difference of the
indicated temperatures, then get out your cal gear and cal
the inputs.
To check for a bad RTD, I'd take an ohmmeter and see if any
leg on the A side has any connection to the B side by
disconnecting the wiring from each analog input and check
the resistance. If there's a low resistance, it indicates
some connection from A to B. If the extension wires are
then disconnected and the resistance is checked on the RTD
lead wires and the resistance remains, then it's a bad RTD.
If the resistance goes high (open circuit) then the
extension wire is shorting or making a low resistance
connection somewhere.
Carl Ellis
Measure First
| Is This Answer Correct ? | 1 Yes | 2 No |
hi... i'm about to learn siemens plc i came across following question in my mind ... plr ans 1. hw motor operated by plc 2. hw drive operated by plc explain dis by both ladder logic diagram and hardware config , connection
what is Analog input/output & Digital input/output,
2 Answers Bapco Bahrain Petroleum Company,
How to do gas analysers calibration in AUTO and Manually by using zero and span gas?
what is the full form of psig.
WHAT IS A CALLIBRATION? WHAT IS MEEAN BY LOOP CHECKING INCLUDES PRESURE, THERMOCOUPLE,TT,DT?
I have flow transmiter DP range is 0 to 5000mmwc,(convert) Display to be show in m3/Hr.
What is the minmum distance between the electrical panel and Instrument panel
Why 4ma - 20ma signal used in instrumentation??
Give me best instrumentation Books name..Ple...
list of flame proof certification ?
If mVolts can drop by resistance of wire as compare to mA, then how thermocouple mV reaches in CCR as accurate value?
What is the three element? And how it work?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)