Dear all... I have 1 0-400 duplex type RTD, I connected the
A side to the temperature indicator and B side to the PLC
panel, but when I have observed then found that The PLC side
temp has the variation. and it was distub to other RTD temp
also. so what can I do.pls help me
Answer / carl_ellis
An offset in readings from separate RTD's can indicate
- a difference in calibration of the analog input devices
- a bad RTD element, one that has drifted out of spec
- a common ground issue with ground loops between the analog
input devices
An RTD is supposed to be ungrounded and the two RTD's in a
duplex element are supposed to be electrically isolated from
one another, so it is unlikely the ground loop is unlikely
unless poor wiring of the extension wire or head wiring has
created a connection to ground.
If you're complaining about a small difference of the
indicated temperatures, then get out your cal gear and cal
the inputs.
To check for a bad RTD, I'd take an ohmmeter and see if any
leg on the A side has any connection to the B side by
disconnecting the wiring from each analog input and check
the resistance. If there's a low resistance, it indicates
some connection from A to B. If the extension wires are
then disconnected and the resistance is checked on the RTD
lead wires and the resistance remains, then it's a bad RTD.
If the resistance goes high (open circuit) then the
extension wire is shorting or making a low resistance
connection somewhere.
Carl Ellis
Measure First
| Is This Answer Correct ? | 1 Yes | 2 No |
What is the difference between conductive lined pipe and conductive unlined pipe? Why do we see that?
0 Answers Process Control Technologies,
What is the difference between bench set and operating range i control valve?
What do you do as a Engineering person EPC for Sizing&Selecting Control Valve?
What is the use of temperature compensation?
in plc source and sink meaning?
In vortex flow meter how can measure the frequency of vortex generated by vortex flow meter
How to calculate the range of level transmitter?
What is intrinsic safety mean.
Why we use negetive (-)voltage in vibration system
Explain, and give a real-world example of MODULATING control
dear friends pls tell me how temperature compensations are done in bourdoun tube of pressure guages thankx
If a control valve is hunting means means if we are giving 50% to the cv, the cv will open at 51% then slowly slwoly it will reaches 49% , so what to do for solve this problem. The cv is double acting and mounted for anti surge operation, it having 4 nos. volume booster, one sov, one positioner, etc..?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)