why 4ma show higher zero ?
i have transmiter flow renge 0-1000 m3/h but 4 ma show in
monitoring 200 m3/h and 20 ma show 1000 m3/h i want when 4ma
show 0 m3/h and 20ma 1000m3/h
Answers were Sorted based on User's Feedback
Answer / automatic
put an offset to avoid the values nears Zero
I mean around 3.99 ma & 4.01 ma, you can do this from a
software, or from coditioning block, or you just shift you
zero to a signifiant flow to rcord.
Is This Answer Correct ? | 2 Yes | 0 No |
Answer / dinesh priyadarshi
1) Set LRV & URV by HART
2) set zero at your desire value by HART
Is This Answer Correct ? | 0 Yes | 0 No |
When a timer is placed in RS Logix 5000 with preset value less than its scan time it is malfunctioning. i.e., if the preset is set to 30ms still the timer TT bit is counting till 150ms(its scan time). Any solution for the problem?
what are the inputs (drawings) we need to prepare loop schematics??
what effects a surging can produce in the compressor
a flow transmitter [range-0-400mbar] connected in process line. please explain me how to calibrate the flow transmitter , & how to do static error
LADDER LOGIC Can any body state Logic on following condition Instructions to use 1-XIC 2-XIO 3-Output ONLY Program Push 1st button On - 1st lamp should On Then Push 1st button Off - 1st Lamp Should remain on Push 2nd button On - 1st lamp should Off and 2nd lamp should On Then Push 2nd button Off - 2nd Lamp Should remain on.
how can you change unit of totalizer in siemens mag 5000 flow meter?
capillary type tranmitter using remote seals and capillary tubes filled with liquid of known of known density so if you wanna callibrate it just close block valve just before capilary @ high side & connect druck apply it's calibrated range pressure as normal calibration ensure low side block valve must be closed & if you asking commissioning so this is not a DP type pressure tx so simple if you wanna put in servie this tx just open high side block valve & than low side block same way i do it but still transmitter showing -13 ma.just tell me what i want to do ?
how the 2.5bar pressure able to control the 40bar steam
8 Answers IBM, PAFL, Thirumalai Chemicals,
without color coding, without nameplate, without multimeter how can you find the type of thermocouple???
can we copy the software from a transmitter using hht(hart 275) ?
what is loop?
cheapest instru-- PMMC, EDM, rectifier, thermocouple.