why using 4-20ma not using 0-20or why not using 1-
20ma???????
Answers were Sorted based on User's Feedback
Answer / chandrasekarapandian
4-20 mA is the universal standard.
Justification:
1. easily splittable ranges 0 % = 4mA
25 % = 8mA
50 % = 12mA
75 % = 16mA
100 % = 20mA
2. 4 to 20 mA passed over 250 ohms coil resistance will
produce a suitable voltage sourcew of 1 to 5 volt.
3. LIVE ZERO
If our sensor to PLC wire connecton is open PLC reads 0mA
where as if the input of sensor in ZERo PLC reads 4mA.
| Is This Answer Correct ? | 14 Yes | 3 No |
Answer / srinivasan narayanan
Most of the Transmitters output used 4 -20mA. This is because to identify whether the transmitters are live or not
if the Transmitter shows 4 mA it's a live Zero
if the Transmitter Shows 0 mA it's a Dead Zero
| Is This Answer Correct ? | 6 Yes | 1 No |
Answer / seshu
when we are using 0 to20ma if any case cable is damage it
carry o ma signal continues so we are using 4 to20 ma
| Is This Answer Correct ? | 5 Yes | 1 No |
Answer / kalpit thakkar
Instrument has own Load of 3mA. so we go for 4-20mA. & Also IEC Approved to 4-20 mA.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / rathod mukesh
0 - 20 ma range is not use in the instrumentaion as standard range because if we use 0 ma for zero process parameter value, if any reason loop wire become break although plc or micro controller get 0 Value at unkown process parameter value and its understand process is in healthy condition but actcully fault is occur in physical data(0-20 ma) transmission link . the plc or micro controller is not accept proper value of process prameter. And we cant define live zero of process parameter. Use to 4- 20 rane ma we easily define live zero.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / rathod mukesh r
If we use 0 - 20 ma rage as standard then we cant define live zero .
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / nilesh
This is a universal standard adopted.4 mA at 0% ensure live
zero.
| Is This Answer Correct ? | 5 Yes | 7 No |
Which boiler is use in power plant
How to force the bit in GE Mark V?
what is meant by calibration
WHAT IS THIS INSTRUMENTATION?
Explain about the leakage class of the control valves
if temperature transmitter is showing wran. sensor 2 fail how can you remove from the transmitter display m/n.3144p rosemount
In Safe Guarding test what means by "Failed to Danger" ?
Will Intergraph support SmartPlant Instrumentation in an AutoCAD or MicroStation environment on a long-term basis?
What is cable size for intrenal wiring in DCS or PLC ,from any card to Terminal amd Why
what is pt100 RTD, and does 100 stands for
What is Positive Calibration and Negative Calibration?
What is the reason for not giving very High Proportional Gain Kp in PID Controller?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)