why using 4-20ma not using 0-20or why not using 1-
20ma???????
Answers were Sorted based on User's Feedback
Answer / chandrasekarapandian
4-20 mA is the universal standard.
Justification:
1. easily splittable ranges 0 % = 4mA
25 % = 8mA
50 % = 12mA
75 % = 16mA
100 % = 20mA
2. 4 to 20 mA passed over 250 ohms coil resistance will
produce a suitable voltage sourcew of 1 to 5 volt.
3. LIVE ZERO
If our sensor to PLC wire connecton is open PLC reads 0mA
where as if the input of sensor in ZERo PLC reads 4mA.
Is This Answer Correct ? | 14 Yes | 3 No |
Answer / srinivasan narayanan
Most of the Transmitters output used 4 -20mA. This is because to identify whether the transmitters are live or not
if the Transmitter shows 4 mA it's a live Zero
if the Transmitter Shows 0 mA it's a Dead Zero
Is This Answer Correct ? | 6 Yes | 1 No |
Answer / seshu
when we are using 0 to20ma if any case cable is damage it
carry o ma signal continues so we are using 4 to20 ma
Is This Answer Correct ? | 5 Yes | 1 No |
Answer / kalpit thakkar
Instrument has own Load of 3mA. so we go for 4-20mA. & Also IEC Approved to 4-20 mA.
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / rathod mukesh
0 - 20 ma range is not use in the instrumentaion as standard range because if we use 0 ma for zero process parameter value, if any reason loop wire become break although plc or micro controller get 0 Value at unkown process parameter value and its understand process is in healthy condition but actcully fault is occur in physical data(0-20 ma) transmission link . the plc or micro controller is not accept proper value of process prameter. And we cant define live zero of process parameter. Use to 4- 20 rane ma we easily define live zero.
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / rathod mukesh r
If we use 0 - 20 ma rage as standard then we cant define live zero .
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / nilesh
This is a universal standard adopted.4 mA at 0% ensure live
zero.
Is This Answer Correct ? | 5 Yes | 7 No |
how to rectify the poor signal strength in utrasonic digtial flow meter ,model:ge digital xce868i
There is a problem with our HART475 it is not communicating with smart devices error becomes "NO DEVICE FOUND"we have insert 250ohm resistance as per requirement but invain plz tell me the solution?
what is easiest way to read STL language in PLC?
Draw block diagram BOILER COMBUSTION loop & Explain
1 Answers Bajaj Hindusthan, Exxaro,
How RAL(Rotary air lock)works in cement industry?
how can i calibrate E & h make conductivity transmiter . unit : mocro siemens Range :0 to 100 micro siemens sensor : capacitive type
You are looking at the RS-485-side of an RS-232/RS-485 converter and the power supply voltage for the converter is +5V. Under idle conditions (no transmission), and assuming you have enabled the RS-485 output: what would you expect at: (a) Output A measured against output B (b) Output A measured against ground (c) Output B measured against ground
what is the Analog signal and what is the Digital signal
Describe the functions of the Operator Interface including the considerations related to alarming and display layout/configuration/layers.
Identification of control valve parts.
0 Answers CCIE, Oil and Gas Jobs,
HELLO FRENDS ,, I M IN THE MIDST OF TROUBLE .. JUST LITTLE HELP ME... SUPPOSE ,, I HAVE A CLOSE VESSELE TANK ( HEXANE MEDIA ) ,, I M USING ROSEMOUNT 2051 DPT FOR LEVEL APPLICATION .. ITS CALIBRATE RANGE IS.. . 0 TO 950 MMH20 ..I DID CALIBRATED DPT WITHOUT REMOVING IMPULSE LINE OF HIGH AND LOW TAPPING.. & WITHOUT DISTURB 3 WAY MANIFOLD..!!! BUT ,,, DURING CALIBRATION I SELECT RANGE BY HART LRV IS 900 MMH20 & URV IS 1300 MMH20 ,, BUT ,TANK LEVEL SOMETIMES 100 % AT 1100 MMH20 , SOMETIMES 1300 MMH20 ..IN THIS CONDITION .. WHOLE LOOP FAILED ,, MAIN THING IS THAT ,, HOW TO CUSTOME RANGE SELECT ?? AND IF I USED RANGE OVER THE ORIGINAL CALIBRATE RANGE ,,,THEN WHAT ERROR WILL BE COME ??? HOW TO ZERO CALIBRATION OF DPT... HOW TO ZERO TRIM BY MANIFOLD ?? AND FOR TANK LEVEL PURPOSE ... WHICH UNIT I CAN USE ??? IS THERE ANY CALCULATION OR CALIBRATION .. IF YEH .. THEN PLZ JUST GIVE ME CALIBRATION STEPS FOR DPT.. THANKS YOURSSSSSSS
what is the different between plc and dcs ? I know full name of this two but I want to know what structure and working style and speed I/O capacity and controller difference?